For Fire Pump rooms located in a basement, that is accessed through a common corridor, is it acceptable to have other rooms (like plantrooms, storage, etc) off the same corridor coming from the staircase to the Fire Pump Room door?
We would provide the required fire resistance rating for the stair, the corridor, and the fire pump room. I'm assuming no storage would be allowed within the corridor itself. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Alex
10/21/2021 07:24:19 am
Hi Anonymous,
Reply
franck
10/21/2021 09:13:03 am
It is possible
Reply
Jack G
10/21/2021 09:24:40 am
The room must have the proper fire resistance rating and correctly required design density.
Reply
Brian Cockburn
10/21/2021 09:43:46 am
As far as I'm aware there's nothing wrong with it, as long as the fire resistance requirements are met. Definitely no storage or anything else obstructing the corridor.
Reply
Todd Wyatt
10/21/2021 10:20:24 am
The 2021 IBC (Section 902 Fire Pump and Riser Room Size & Section 913 Fire Pumps) does not require the corridor accessing the fire pump room (FPR) to be protected with fire-resistance rated (FRR) assemblies unless required by the building's occupancy classification, the occupant load served by the coridor, and if the building is protected by an autmomatic sprinkler system as indicated by Table 1020.2. The FRR of the FPR is required to be 2-Hour Fire Barriers (2FB) or 2-Hour Horizontal Assemblies (2HA) unless the non-High-Rise Building is protected by an automatic sprinkler system and then the ratings can be reduced to 1-Hour FRR.
Reply
Jay
10/27/2021 03:41:49 pm
IBC section 913 requires fire pumps to be installed in accordance with NFPA 20. NFPA 20 requires fire pump rooms to be directly accessed from the exterior of the building or via a FRR passageway from a FRR stairway.
Reply
Anthony
11/3/2021 08:28:39 am
Where does 20 say the pump must be accessible from the exterior?
Jessica Lutz
10/21/2021 12:23:38 pm
I've see this issue many times.
Reply
Mike
10/21/2021 06:59:26 pm
Consult with the AHJ. Many that I've worked with don't allow a pump in a basement, especially a diesel, because of problems with access to the fuel tank and refueling.
Reply
sean
12/31/2021 06:54:24 pm
is it really the AHJ or the owner/designer/contractors not wanting to pay the extra costs those involved.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |