Can "open parking garages" be located below high rise buildings?
If so, can the standpipes for the parking garage be manual dry and can sprinklers be omitted in the portion of the building considered an open-garage expect for the level directly below the high-rise occupancy? Trying to get some big-picture understanding here, thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
3/22/2023 06:55:04 am
As long as the parking garage meets all IBC definitions for an "open parking garage" (around section 406) and your state still adopts older code that allows for an omission of sprinklers in open parking garages... yeah, you can get away with it and your state still allows an older edition of IBC that allows for an omission in parking garages.
Reply
Franck
3/22/2023 08:27:54 am
If the question is "is it mandatory to have sprinkler protection?", then Pete answered quite clearly and the answer is probably no (might depend on your AHJ).
Reply
Todd E Wyatt
3/22/2023 09:00:12 am
SUMMARY
Reply
Todd E Wyatt
3/22/2023 09:00:42 am
REFERENCES
Reply
Todd E Wyatt
3/22/2023 09:01:27 am
REFERENCES continued ...
Reply
Casey Milhorn
3/22/2023 09:03:44 am
I agree with Franck. I hate to even think about 20 years from now and there's a garage full of lithium ion batteries in an unsprinklered area, right under a hi-rise full of people.
Reply
Glenn Berger
3/22/2023 12:25:20 pm
To the question "Can an open parking garages" be located below high rise buildings?"
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |