We are working on a 20-story apartment building where the corridors are open with parapet walls on either side. These serve as an exit access corridor. The project is under NFPA 101.
In Chapter 7 of NFPA 101, the exist access corridor is supposed to have a minimum fire resistance rating of 1-hour. However, I can't seem to find any provision in the code regarding open corridors. Will these corridors be required to have a fire resistance rating? What about the doors of the dwelling units? I'm assuming if the corridor is not fire rated, then we wouldn't need opening protection through these partitions/walls. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
chad
9/7/2022 06:49:10 am
The corridors are open to an atrium, is that what you mean?
Reply
Alex
9/7/2022 07:48:58 am
Hi,
Reply
DS
9/7/2022 08:12:22 am
7.5.3 Exterior Ways of Exit Access
Reply
edward Ferraioli
9/7/2022 08:26:21 am
Im in nj code. Full sprinkler building corridors are rated 30 minutes 20 minute fire door. Not sorinklered 1 hour. Open to atrium what ever attruim rating is. If open to atrium the atrium smoke control must be able to handle corridors also in there smoke test.
Reply
Ed James Ferraioli
9/7/2022 08:29:58 am
Look in IBC 2018 section 1020 I'm using nj edition it also in international IBC around same section
Reply
Todd E Wyatt
9/7/2022 08:30:25 am
NFPA 101 Life Safety Code is organized by general chapters (1-11, 43) and chapters (12-42) based on Occupancy Classifications (OC). Chapter 11 Special Structures and High-Rise Buildings includes requirements for “high-rise buildings” (HRB).
Reply
Jamal
9/7/2022 08:34:37 am
Open Areas corridor/ Door / Walls NOT required to be Fire Rated Material . The Material selection shall be Flame spread index 0- 25 since high rise , whereas the material of cement and bricks comes under 0-25 FSI . Solid Block Bricks are automatically 2 Fire Rated .
Reply
Jesse
9/7/2022 08:37:48 am
Are these open corridors open to an atrium? Or are they open to atmosphere? If open to atmosphere, I wouldn't think the fire rating requirement to apply.
Reply
schulman
9/7/2022 08:46:56 am
i cannot think of a single instance of what you described, regardless of atrium, etc.., where the penetrations would not be required to be rated.
Reply
Glenn Berger
9/7/2022 08:52:12 am
What I interpret in your question is that you really do not have exit corridors or exit access corridors as defined by NFPA 101. You have aisleways that lead to an exit (stairway). The walls of the dwelling units need to be rated.
Reply
Tim
9/8/2022 12:41:12 am
The separating walls between units must be fire rated 60 minutes. The passages if open and ventilated will not pose a problem provided you have the option to travel in two directions to a protected stair.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |