We have a project where a foam-water system is installed for two generator rooms. The rooms are on the same floor and some distance from each other, which is also on the same floor as the fire pump, which is served by a vertical foam bladder tank.
I've read here before that it's possible to have one proportioner serving both of them, but is it possible to have one deluge valve to serve both rooms? If so, do I need to add motorized butterfly valves to regulate the flow direction? Really appreciate the input. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Dan Wilder
8/4/2023 08:00:32 am
No issue with serving multiple areas from the same valve, proportioner, or system overall as long as the owner understands that if one system goes off...both rooms are getting a bubble bath. Typically, that is motive enough to have separate valves controlling each room.
Reply
Anthony
8/4/2023 08:08:45 am
Dan should get extra points for "bubble bath."
Reply
Jesse
8/4/2023 08:09:07 am
The installation as you described it is code-compliant, and I've seen it before, but isn't really advisable. If the generator rooms are critical to operations, you could have a prolonged interruption if one system trips because both rooms will be filled.
Reply
Glenn Berger
8/4/2023 08:19:07 am
1) Are you planning for pre-action foam systems or deluge foam systems? If deluge then the double bubble bath scenario is appropriate.
Reply
Casey Milhorn
8/4/2023 08:19:56 am
I agree with everyone as well. Definitely a no on the solenoid control valves, bad idea. I don't know the size of each room, but flowing both at once in a calculation is bound to lead to a larger valve, bulk feed main, possibly some balancing hoops to jump through if they aren't equal size and equal distances from the deluge valve. I think I would have to choose what I would imagine are two smaller deluge valves over one large deluge valve. If the deluge valves end up in the pump room, or adjacent to each other in a shared closet, I believe you can share one releasing panel if you are going with a modern deluge setup using heat detectors or similar triggers.
Reply
David Kendrick
8/4/2023 09:52:08 am
Question: Is the system open head or closed head?
Reply
Mark Harris
8/4/2023 11:27:16 am
Adding to the detection comments if you did this as one zone with the rooms far apart owner and first responders will not know which room caused the system to trip. With an intelligent detection system that could be mapped so each room gave notification and tripped the single deluge valve solenoid but I agree with the other comments that two deluge valves make more sense.
Reply
I’m not looking at the rules here; “I’m looking at the overall practicality of the building-wide fire protection. These are questions that I would ask when trying to figure out whether the foam-water systems for the two rooms should be totally separated, or somehow combined.
Reply
Pete D.
8/13/2023 08:06:24 am
I've designed 2 control areas on 1 system valve before. Whatever the foam system area ends up being, you need to do the demand calc to prove the water density delivery. Then you need to do a source calc to size the bladder tank and buy the foam concentrate. In a real flowing scenario, supply pressure - friction loss - pressure at the flowing orifices = zero. It's not as if the sprinkler system achieves the design pressure and then throttles itself. Many folks forget this and undersized their tank or don't buy enough foam.
Reply
Tahasin Khan Mohammed
11/12/2023 01:46:24 am
foam bladder tank location in generator room it's allowed or not as per NFPA
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |