Is "tenting" wet system piping (in an unheated attic) an appropriate approach to protect the pipes when the outside air temperature can drop to approximately 0 degrees F for multiple consecutive days?
In this case, the soffit and ridge vents allow exterior air into the attic space and there is no air barrier to prevent cold air infiltration. I have reviewed NFPA 13 and 13R and cannot find a definitive answer. Many thanks for assisting. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Anthony
4/1/2024 07:54:13 am
It's appropriate if you have sufficient insulation above and heating bleed through form below.
Reply
Dan Wilder
4/1/2024 08:09:13 am
The installation is to be in warm areas, not subject to freezing, or provide means to avoid freezing (antifreeze, tenting, dry system, heat trace, circulating, heat loss calculation) is defined within 16.4.1 (19' Ed). It's up to the installer to comply with the warm space installation as required per NFPA.
Reply
RayJ
4/1/2024 08:18:09 am
Here in IL, or as I call it, the land of ice and snow, the best way to protect the pipes is a dry system. No matter how much tenting and insulation you have, all it takes is for someone to forget to replace the insulation.
Reply
S
4/1/2024 08:35:43 am
ND = Frozen Tundra. I would say any area where temps drop below 30 degrees for consecutive days (especially where wind flows through the attic) a dry system is the only way to go. Tenting is a joke because the insulation required never stays put. IMO
Reply
Glenn Berger
4/1/2024 09:28:09 am
Tenting sounds like a good engineering approach until the first time the system freezes and then breaks. Once this happens, then the approach of never again will be utilized.
Reply
Jesse
4/1/2024 09:53:16 am
It is appropriate, but I'd probably want to see a heat-loss to support it.
Reply
Jack G
4/1/2024 10:14:04 am
First rule of Fire Protection- wet systems :
Reply
Pete H
4/1/2024 12:50:00 pm
In NFPA 13R (2016 edition)
Reply
S
4/1/2024 01:13:04 pm
Correct me if I'm wrong, but I believe this is only for an area above the ceiling and 'not' in the attic space. Insulation over piping in the attic space will not stop the water in the pipe from freezing in North Dakota, so I imagine it is the same in any place above the freeze line? I think there may need to be a separation between the two areas, pipe in the joist vs attic space. Maybe separated by sheet rock or plywood?
Reply
Pete H
4/1/2024 01:40:34 pm
The exact ruling is that piping covered by insulation as shown in those diagrams is part of the area below the ceiling and not part of the unheated attic area.
Pete H
4/1/2024 01:42:09 pm
For reference, the area above the blown in insulation on A.5.4.2(f) is labelled "unheated attic space"
S
4/1/2024 01:55:59 pm
Thank you Pete.
Dewayne Martinez
4/2/2024 12:54:11 pm
In the past on 13R projects we have had the GC make a "box out" of the pipe with the blue polystyrene insulation board, add some grill registers in the ceiling below to transmit some heat and then have the insulation contractor provide what they felt was enough insulation on top to maintain 40F.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
April 2024
PE PREP SERIES |