I'm working on a a high-end hotel which will have a vertical turbine fire pump above a water storage tank.
Can we waive a minimum pump submerge depth by installing an anti-vortex plate between the pump's bell and the strainer? The fire pump is a 1,500 gpm vertical-turbine type, located directly above the water tank. The tank depth is 6'-3" from the overflow bottom down to the tank floor. The water tank area is 2,408 sqft. The selected pump recommends 51.63-inches as a minimum submerge depth. This is in addition to a 12-inch clearance between the bottom of the strainer and the tank floor. The water level to be maintained inside the tank then must be 63.63-inches (95,511 gallons). The remaining active volume in the tank after extracting the required volume will be 112,582 - 95,511 = 17,071 gallons. This is not enough to run the pump set for the required time under NFPA 13 2019 (Table 19.3.2.1 and 19.3.3.1.2). Can adding an anti-vortex plate between the pump's bell and the strainer waive this minimum submerge depth? If not, what might be a recommended solution for this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Connor
4/14/2021 08:20:25 am
The easiest solution is to construct a pit to accommodate the pump shaft. That way your submergence depth is met without having to deepen the entire tank. As long as you have enough water above the minimum submergence point on the shaft to meet your entire duration, you're good.
Reply
Rusty Scott
4/14/2021 11:18:21 am
Agreed, we use pits to get it below the submergence depth requirements. Per our pump manufacturer rep, the pit also aids in vortex issues.
Reply
Jesse
4/14/2021 02:37:27 pm
Agree with the pit solution. I think that may be your best, if not only option for this specific pump
Reply
David Williams
4/15/2021 01:43:06 pm
Many fiberglass tank manufacturers will also provide (at a cost of course) an internal “sump” that allows the intake bell to be low enough to use “all” off the tank capacity is you don’t have room to add a separate wet well.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |