When applying NFPA 13R to a mixed-occupancy (R-2 and S-2) building, what is the definition of "incidental"?
The building in question is three stories of residential over a parking garage designated for residents only. Each residential floor is approximately 2,000 sqft and the garage is approximately 3,000 sqft. The building is type V-A (wood, combustible) throughout. IBC 2015 Section 509 defines incidental as constituting less than 10% of a given floor. Does this entire building require a full NFPA 13 system? If possible, please provide a code basis, thank you! Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Dan Wilder
1/15/2021 08:10:19 am
Big rabbit hole of confusion but your question starts with what is considered "incidental" and provided the correct building code definition but transitions to if the building requires a full 13 system vs 13R which is separate from incidental use areas as they pertain to NFPA (an example being small ordinary hazard areas within a floor that has a light hazard calc).
Reply
Ryan J
1/15/2021 09:07:55 am
Section 903.3.1.2 of the 2015 IBC may be able to point you in the right direction for this issue.
Reply
sean
1/15/2021 09:16:18 am
The building code determines which standard(s) you can use for a given project.
Reply
Anonymous
1/20/2021 05:22:06 pm
We do many projects like this in Massachusetts where the state amendment to the occupancy table 903.2 reads,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |