In the introduction (Origin and Development) to the 2023 Ed. of NFPA 25, it mentions that several changes have been made to Chapter 5, "such as additional requirements to remove concealed sprinkler cover plates and inspect the sprinklers". I have scoured the text of Chapter 5, and cannot find this requirement anywhere.
Was this discussed but not implemented? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Dan Wilder
1/23/2023 06:51:54 am
If you go to the NFPA site and review the "Archived Revision Information" section at the bottom of any NFPA, it will go through all the revisions and their accepted/rejected status as it goes through the public input and committee meetings. You can then see the process and reasons items are proposed and even comments made by approving or rejecting voting members. It's a little overwhelming to start but the format is understandable after a bit. Just start to look/search for words "cover", "plate" in this case, then you'll see new proposed sections "5.2.1.1.1", and work into the CAM's (had to look at the final voting then to the CAM's).
Reply
1/23/2023 11:35:36 am
Great stuff Dan! I did try to go through the development information as much as possible, however as you say, it was a bit overwhelming. I appreciate your insight as to how to navigate it next time. Thank you!
Reply
Anthony
1/23/2023 08:08:26 am
Dan Nailed it.
Reply
Todd E Wyatt
1/23/2023 08:15:44 am
If you access NFPA documents via NFPA LiNK, the "new" portions of the NFPA documents are highlighted (see "x" below) ...
Reply
Todd E Wyatt
1/23/2023 08:20:08 am
2023 NFPA 25 ... (4) references to "escutcheons" & (1) to "coverplates" in Chapter 5 :
Reply
Eric R
1/23/2023 08:24:04 am
Got to feel bad for the staff editors that have to prepare a book for print that is subject to change at the very last minute lol.
Reply
1/23/2023 11:41:53 am
For sure Dan, and how many of us dig into the text of the Origin and Development to find that type of discrepancy!
Reply
Matthew Mueller
1/23/2023 11:43:26 am
Erik, not Dan. Whoops!
Pete H
1/23/2023 12:34:27 pm
Given how many jobs I've shown up that where I've seen concealed plates... that don't actually have any heads behind them (think I can count it on two hands., but one hand might not be enough).... this might not be the worst thing to add if they decided to add it. I kind of hope they do later since it didn't make it in this round.
Reply
Dan Wilder
1/23/2023 04:15:43 pm
This should be an acceptance testing requirement or part of the inspection process during construction. After 5 years (without a major loss) it's gone on 5 years too long....
Reply
Jess Lutz
2/1/2023 03:58:22 am
I concur.
Pete D
1/23/2023 07:42:11 pm
I've discovered many errata in NFPA standards, I stopped reporting them. I also discovered arithmetic errors in the NFPA and SFPE Handbooks. I did get a kick, as a young engineer, out of emailing them to let them know the rule on raising a power to another power. Strictly regarding the standards, they're only mistakes for 3 years... So, there's that.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |