For seismic bracing, can one lateral and one longitudinal brace, attached within 2-foot of a drop to the floor below, be considered a 4-way brace?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
JI
3/22/2022 08:20:09 am
Yes, it most likely is acceptable. FM Data Sheet 2-8 show many example situations like this. While is is not the NFPA standard, I find DS 2-8 is much more stringent and therefore it is good to read due to the better examples and pictures provided.
Reply
Alex
3/22/2022 01:05:19 pm
I agree with JL here. FM data sheets tend to provide great examples/pictures.
Reply
Jesse
3/22/2022 08:25:18 am
Agree with Jl.
Reply
Casey Milhorn
3/22/2022 09:25:50 am
I second the opinion as well. Seismic bracing does have some room for interpretation and for myself over the years I find a little common sense goes a long way. Not that the standards aren't mostly clear, but just like with underground pipe and fitting restraint, understanding the intent and end goal goes a long way in understanding why the rules are there and how to deal with different situations. Great question!
Reply
Brian Gerdwagen FPE
3/22/2022 09:31:10 am
You need to make sure that there is not a flexible coupling between the brace and the drop.
Reply
3/22/2022 10:51:20 am
Brian, doesn't NFPA-13 (2016) Figure A9.3.2(a) allows the brace to be provided either above or below the flex coupling on the riser? It seems like either configuration is acceptable, right?
Reply
SCHULMAN
3/22/2022 10:17:08 am
good point by Brian ...
Reply
Manny Rios
3/22/2022 10:59:00 am
Good Morning!
Reply
Patrick Nelligan
3/22/2022 12:50:24 pm
NFPA 13-2016 definition is: 3.11.3* Four-Way Bracing. Adjacent sway braces or a sway brace assembly intended to resist differential movement of the system piping in all horizontal directions.
Reply
sean
3/22/2022 07:37:20 pm
I like FM as much as the next guy but I don't like their development process.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |