We have a project where a control module is connected to the mechanical controls that is programmed to the variable frequency drive for a fan on a large unit. When a duct detector senses smoke, the control module (which is normally-open circuit) will close the circuit, sending a signal to the mechanical controls which shuts down the unit.
On this project we had a bad set of control modules that didn't work. We discovered this in testing with the local jurisdiction, and swapped out the modules and the system now works correctly. Both the jurisdiction and I wondered whether this normally-open arrangement is acceptable. If a control module were to fail, the duct detector would not be able to close the circuit on the module and the fan would remain running. In this scenario, there would be no supervision or way to know that the control module failed other than someone standing at the fan or finding the issue during testing. My inclination is that in the future these modules could be normally-closed and open upon duct detection. That way if the module fails and opens on its own, the unit will shutdown in a "failure" mode. Is it code required that this arrangement be fail-safe? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments
MIKE R
5/10/2019 10:12:20 am
Control wire should be normally closed, so it is fail safe.
Reply
WES
5/10/2019 10:52:38 am
I would agree with Mike.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |