Is there a requirement to monitor a fire pump or fire protection sprinkler riser room's temperature with the fire alarm system?
It is clear from NFPA 72 that the device needs to be added to the fire alarm panel if it is present. NFPA 13, 14, and 20 don't seem to have a need to monitor the room's temperature. From NFPA 72 (2016 Edition): Section 17.16.5 Room Temperature Supervisory Signal - Initiating Device. A room temperature supervisory device shall indicate a decrease in room temperature to 40 degrees (4.4 C) and its restoration to above 40-degrees (4.4 C). Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Dan Wilder
12/14/2021 07:25:15 am
There is no requirement to monitor the air temp, just to maintain at or above 40°F (20-19' Ed) 4.14.3 with an "approved or listed" source of heat - possibly higher for diesel applications. The book does provide annex language that are recommendations in A.4.26
Reply
Alex
12/14/2021 08:07:09 am
The temperature does not need to be tied into the FACP, just needs to be maintained above 40F. Having the temperature tied into a monitored system is good practice though!
Reply
Max Sing
12/14/2021 08:08:30 am
For an exterior room containing dry pipe equipment I spec'd out a room temperature switch that has a 40 degree threshold that is made by a common fire protection company. They seem affordable and might meeting what you need even if not an exterior room while also not increasing budget much. Just google "NFPA 72 Room Temperature Switch" was the first option.
Reply
AHJ
8/2/2023 03:33:10 pm
This was a very helpful suggestion, thank you!
Reply
Glenn Berger
12/14/2021 08:16:48 am
It is not a written requirement to provide the switch and therefore monitor the switch. However depending on the project location it SHOULD BE A REQUIREMENT to provide and monitor by a system that has a constantly attended location.
Reply
Jesse
12/14/2021 10:08:11 am
The requirement is to maintain above 40-deg F, not necessarily to monitor it
Reply
Phil W
12/14/2021 11:15:31 am
NFPA 20, A4.26 states that there are other conditions for which such signals might be recommended, depending upon local conditions. Some of those conditions are.
Reply
sean
12/31/2021 06:33:01 pm
no req. to monitor.
Reply
Dan
1/23/2024 02:12:20 pm
Is there a definitive mounting height or location for these RTS?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |