In a 15-story highrise building, can the standpipe system be zoned with an Automatic Dry in the 1st -5th floors of the unheated Parking Garage, and an Automatic Wet in the 6th- 15th floors of the heated office portion?
Are we allowed to mix types? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Casey Milhorn
3/22/2024 08:17:55 am
I've designed one that way before. I don't think I've ever seen anything that says you can't unless there is something in the applicable building code. Below is from 2013 edition of NFPA 14.
Reply
Dan Wilder
3/22/2024 08:43:00 am
You've used the correct terms....automatic...for both. Just make sure they comply with the Class I requirements. No different than providing a sprinkler system that is wet for a portion and dry for a portion.
Reply
4/2/2024 03:39:24 pm
DAN WILDER- Do you know where I can find the 3 minute delivery requirement you are referenceing? Thanks,
Reply
Jack G
3/22/2024 01:31:33 pm
In my opinion the above statements are correct.
Reply
Glenn Berger
3/23/2024 01:05:51 pm
The design appears to be compliant.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
April 2024
PE PREP SERIES |