NFPA 13 (2019) Section 9.4.3.2 states that quick-response sprinklers shall not be mixed with any standard-response within a compartment unless some conditions apply.
Section 9.4.3.2 Where quick-response sprinklers are installed, all sprinklers within a compartment shall be quick-response unless otherwise permitted in 9.4.3.3, 9.4.3.4, or 9.4.3.5. If a quick-response sprinkler is a type of fast-response sprinkler, then not all fast-response sprinklers are quick response. So my question is: can I mix standard-response with fast-response heads? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
2/27/2024 06:38:56 am
Depends if the fast response sprinkler is listed as quick response or not.
Reply
Dan Wilder
2/27/2024 07:04:19 am
Yes, but only if you meet one of the exception criteria. A good example would be an overhead system with standard response sprinklers and in-racks utilizing fast response (Section 25.1.6.3 & 25.6.2.2 for example)
Reply
Anthony
2/27/2024 08:15:22 am
What does mixing mean in this instant? can one portion of a warehouse be ESFR and one be OH2, sure.
Reply
Glenn Berger
2/27/2024 08:23:42 am
IMO, It is not proper to mix sprinkler types (response or orifice types) within a "compartment." Unless you want to provide the building owner with zero flexibility to adapt the compartment to meet the Owner needs.
Reply
Jeremy S
2/27/2024 11:01:14 am
I have a situation where a warehouse has an existing ESFR system. The tenant is splitting the building and adding a Riser Room to separate the space. This riser room has caused the ESFR heads to be over spaced from the new wall. There isn't enough room to properly space ESFR head to this wall.
Reply
Glenn Berger
2/28/2024 08:19:05 am
Where walls are modified, the sprinkler system on both sides of the new construction needs to be evaluated. The storage side would need ESFR sprinklers and the Riser Room being in a separate compartment it can have stand response standard sprinklers.
Jesse
2/27/2024 02:19:40 pm
Yes and no.
Reply
Franck
2/27/2024 03:03:20 pm
NFPA 13 is very clear on that specific topic.
Reply
Rob B
2/28/2024 07:37:50 am
This is spot on
Reply