Is there a minimum ceiling height that would be required for a Fire Pump Room?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
schulman
8/12/2022 08:12:23 am
honestly don't think you will find anything in NFPA - somebody please prove me wrong ...
Reply
RBriggs
8/12/2022 08:16:47 am
I agree with Schulman, no ceiling height requirements that I know of; but I don't think I have ever seen a ceiling in a Fire Pump room, no need for it.
Reply
Glenn Berger
8/12/2022 08:19:09 am
The minimum height of the space is dependent on what is being accomplished in the pump design. Is there a pump bypass provided? Is there a interior round-the-pump metering/testing assembly?
Reply
Todd E Wyatt
8/12/2022 08:28:37 am
Minimum ceiling heights depend on the applicable Code and how the AHJ defines a Fire Pump Room (FPR) :
Reply
Brian Hoole
8/12/2022 12:42:05 pm
Keep in mind that the door to a pump room should be at least 4 feet wide and 7 feet tall. Of course the door frame requires space so any pump room should have a ceiling of 7'-6" or more just to allow for the door structure.
Reply
Patrick
8/12/2022 06:23:23 pm
And NFPA 70 requirements in the previously issued forum:
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |