We're designing a Wet Manual Class I standpipe in a low-rise building with 4 stairs/standpipes and therefore 4 isolation valves. There are 7 total levels of this building.
The horizontal supply pipe must be located in the level 5 ceiling. Is it allowable to locate the standpipe isolation valves at this 5th level versus the more typical location near the bottom of each standpipe? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Alex
6/21/2022 06:57:19 am
NFPA 14 (2013) 6.3.2 states that valves shall be provided on all standpipes to allow for isolation of a standpipe without interrupting the supply to other standpipes from the same source of supply.
Reply
Gopal PK
6/21/2022 11:16:22 am
Hi Alex
Reply
Jesse
6/21/2022 08:17:24 am
The only issue I would see is accessibility. The isolation valves must be accessible to trained personnel during an emergency situation. If it is readily accessible, I wouldn't see an issue.
Reply
Anthony
6/21/2022 10:33:38 am
Totally allowable, do it all the time.
Reply
Glenn Berger
6/21/2022 01:48:33 pm
May be unusual, but not specifically prohibited.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |