I have a question about using galvanized pipe in wet-pipe systems. I have a building in which part of the building is wet-pipe, and part of it has a dry-pipe system using galvanized pipe in an unheated area.
Our renovation of the building is turning this space into a heated area. My initial thought was just leave the existing pipe in place, convert the riser to wet-pipe, and make any minor modifications to the system coverage as needed. As I've read more I'm not so sure. FM specifically says not to use pipe that has been internally galvanized on a wet-pipe system, and while it doesn't seem to be outright prohibited by other sources, I seem some strong recommendations against it. If there is any experience out there on the subject I'd appreciate it. At the moment I'm strongly considering replacing all system components and materials back to the base of the riser. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
9/20/2022 07:49:28 am
If you want a very angry client in as little as a couple months to a couple years, leave the galvanized.....eeck. While N2 inerting and addition of high point air vents will "slow" the process down, depending on the water supply, the pipe will develop leaks fairly quickly.
Reply
Alex
9/20/2022 08:20:39 am
Replace the pipe all together.
Reply
Alex Riley
9/20/2022 08:54:51 am
Hi,
Reply
Glenn Berger
9/20/2022 09:08:23 am
I would love to say replace it all. How big of a project do you have? A full replacement will be no small task.
Reply
schulman
9/20/2022 09:15:32 am
galv pipe corrodes and leaks faster
Reply
Franck
9/20/2022 09:22:22 am
Just to confirm other comments : never use galvanized pipes for wet sprinkler systems and for areas where the ambient temperature could exceed 130°F.
Reply
Julio Solar
7/20/2023 10:18:14 am
I understand, but we are by the sea (Florida) and our system is completely wet. We are having a lot of leaks due to corrosion in the black piping. As we repair them, we are doing it with galvanized. Again: our sistem is wet with pump and jockey pump with 150psi. Is it fine to use galvanized in a wet system? Thank you guys.
Reply
Pete H
9/20/2022 10:17:19 am
Replace the pipe if it's an FM job or if the pipe was originally submitted to FM specifications rather than UL listing. Replace the pipe if it's a "best practice" job. Replace the pipe if you have the money and the client wants to avoid leaks.
Reply
DAVE
9/20/2022 11:34:58 am
I especially agree with Pete's answer here, as it is realistic by mentioning "best practice" and the client's money. I believe the owner should be made aware of the issues and risks so they can make an informed decision based on their situation, budget, and timeline. And document. But I think that's why the original question asked if there was any experience on the subject. As long as I have been in the business, I still rely on my most experianced field guys at times like this.
Reply
Jon
9/20/2022 06:05:30 pm
Well here in Saudi Arabia, galvanized pipe is common for wet sprinkler system. Pipe is hot dipped galvanized and we don't see any problem with leakage or corrosion. It is also sometimes being recommended in the project requirements
Reply
Chris
9/21/2022 07:57:00 am
If you're talking just a couple pieces I would switch it out without too much fuss. If you're talking about a pretty sizable amount then I would suggest having a conversation with the owner and putting the ball in their court. Personally I cant think of any projects where we had an issue with galvanized pipe on a wet system, the only issues we had were on dry systems.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |