I’m a Fire Inspector/Design Reviewer and I have a problem that I’ve been trying to tackle. NFPA 14 systems are designed for high volume low pressure firefighting tactics, but the majority of fire departments in America use high pressure low volume equipment. Here are the key points:
NFPA 14 Type 1 standpipe systems provide 250 gpm at 100 psi with 200 ft to most remote location in a sprinkled building. In the firefighting world this equates to a fire attack with 250 ft of 2.5” hose and a 1-1/8” smooth bore nozzle. The 250 ft comes from, 50 ft to stretch to the hose connection on the floor below the fire floor and 200 ft to most remote location on the fire floor. Fire ground friction loss calculations for 250 gpm through 2.5” hose is 15 psi loss per 100 ft. A smooth bore nozzle requires 50 psi to operate properly. We are stretching from the floor below so we have roughly 6 psi head loss. So the required pressure at the hose valve is 93.5 psi. You can see that the NFPA 14 design requirements are in line with the use of this higher volume lower pressure equipment. The problem is that 2.5” hose is very heavy and requires a lot of man power. 2.5” attach lines are used by large city departments like Seattle, New York, and Chicago. Many smaller city and town departments don’t have the staffing to stretch such big lines. We may only have a couple firefighters stretching an attack line where as the big cities would have 6 or more. So we use smaller more maneuverable hose and more pressure demanding fog nozzles. A more typical firefighting set up in the majority of fire departments would be 1.75” or 2” hose and a 75 psi or 100 psi fog nozzle flowing between 150-200 gpm. I’ll use Bozeman as an example. We use 1.75” hose, a 75 psi fog nozzle, and a target flow of 175 gpm. In our experience the pressure loss per 100-ft of 1.75” hose with 175 gpm is 50 psi. So if we need to stretch 250 ft of hose, we would need 206 psi at the hose valve on the landing below the fire floor. Add in that the tallest building we have is 11 stories, and a 25 psi pressure loss adjustment for pumping the FDC, and we are up to 285 psi required at the FDC. There seems to be a disconnect between the design world and the firefighting world. This poses all sorts of problems such as compromising sprinkler systems and old standpipe systems since they may have components that are not rated for such high pressures. Even worse are systems with pressure reducing hose valves that wouldn’t even allow us to pump the FDC to get anywhere near the pressures we need with our equipment (see One Meridian Plaza fire in Philadelphia). I think that Fire Departments need to communicate their design needs to designers, and Fire Departments also need to look at the equipment they use, and see how they can make changes to operate more closely to what NFPA 14 systems are designed for. If you have any knowledge on this topic I would love to hear it, thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Dan Wilder
6/26/2020 08:26:26 am
This sounds more like the need for the NFPA 14 Committees to have Public Inputs pushed to them to account for these types of requirements OR having your local Building/Fire Codes amended accordingly.
Reply
Jonathan Joseph
6/26/2020 10:25:09 am
In California we have a California Fire Code and are hose pull is greatly decreased. Fire departments use 2 1/2 in hoses that 100ft and with the 250 gpm and 100 psi the nozzles spray 30ft. minimum
Reply
David Hartrman
6/27/2020 10:05:16 pm
Thank you. Reducing distance from hose valve to most remote areas in sprinkled buildings from 200 ft to 150 ft would definitely make a difference.
Reply
Brian Gerdwagen FPE
6/26/2020 10:32:46 am
This requirement is to provide the fire department with something before the truck shows up and boosts the pressure. There is also no way that the fittings installed will handle 285 psi at the FDC. You can make an 11 story building work without a PRV. It will be close, but the usual break point is 12 stories. You may begin to have the 175# rated fittings fail if you have an older building.
Reply
Glenn Berger
6/26/2020 10:33:31 am
The local Fire Department requirement needs to be clear to the Design and/or Construct working in that municipality. I have seen this done as City Amendments to the State and National Building and Fire Codes. Also each system designer should have a meeting with their corresponding city official to understand local conditions.
Reply
Rob Bambino
6/26/2020 10:39:52 am
250' of hose for an interior attack is a bit much. Generally, 150' is the reach of the hose, and that is why we would require intermediate hose connections on the floor if the hose stretch exceeds the 150 from the stairwell. With that in mind, at 150' of 1 3/4 hose with a adjustable nozzle would be much less than your 285 figure, and generally at 100' for 1 3/4 its a 30psi loss.
Reply
David
6/27/2020 10:02:10 pm
Thank you very much for your input on this. I agree that a 250 ft stretch is a tall order and a worst case scenario.
Reply
Fred
6/29/2020 07:31:44 am
Fire Departments should not be using higher pressure fog nozzles on their high rise packs for many of the reasons you mentioned. Higher pressure such as 100 psi at the tip vs 50 psi on a smooth bore. Their have been LODD due to this type of setup over the years and it is not advised and frowned upon in the fire service today. Besides pressure another issue is debris in the system can clog and restrict water flow in fog nozzle where the smooth bore will pass most debris. Some departments that use 1.75" as high rise hose need to understand the flows in buildings in their jurisdiction, so maybe it works for them, but at least use a smooth bore for a lower operating pressure and debris possibility. Some departments are switching to 2" hose with 2.5" couplings for lower operating pressures and higher flow, as typical 2" hose has only 1.5" couplings.
Reply
6/29/2020 06:58:45 pm
1. Hooking up the on floor below. This is a historical practice rooted in the open stairwells of the past. I find it unlikely you are operating in tenement-like conditions. You are in a rated stairwell, inspected by a stalwart building inspector, with maintenance inspection by a steely eyed fire inspector. There is a least one rated door between you and the fire. The fire inspector ensured even the smoke seal is in place. Hook up on the fire floor. Save 50’ of hose. Advance your FD into the ‘80’s.
Reply
Jessica L.
7/1/2020 10:52:00 am
Thank you all so much for sharing this conversation!
Reply
Chris Baker
4/22/2024 11:35:51 am
Do we really need that extra 25psi for pumping the FDC if we aren't flowing upwards of 1400lpm/370ish US Gal, though?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |