Is Unistrut allowed to be used for trapeze braces on sprinkler systems?
There are two issues at hand - one is making sure the section modulus allows for Unistrut to be used. In this case we have a 16-inch span with only a 2-1/2" main on the trapeze, so we're good there. The other issue is the listing and approval of components. Any tips here? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
20 Comments
Pete
7/22/2021 06:22:18 am
I think the MeyerFire Trapeze sizer tool can specifically help you with sizing Unistrut as trapeze as well as having items from the Unistrut Catalog noted.
Reply
Bob Kluck
7/22/2021 08:32:47 am
It can, however if you don't have that package, the data sheets for Unistrut or Approved Equal Competitors specify the section modulus. If you look that up for the one you plan to use, you should be able to determine if it meets the requirement for NFPA 13.
Reply
Glenn Berger
7/22/2021 09:18:02 am
Using Unistrut or similar products are fine. Just provide the catalog data and calculations for the intended use and you will be fine.
Reply
Craig Hanson
7/22/2021 09:24:51 am
Although Unistrut can be used, Unistrut pipe clamps are not listed for use for fire sprinkler systems [NFPA 13 2016 : 9.1.1.5.1, see handbook notes]. additionally unistrut spring nuts cannot be used for trapeze hangers [NFPA 13: 9.1.1.7.8] double nuts and washers need to be used. I hope this helps.
Reply
Darrel Jacobs
7/22/2021 12:05:46 pm
Craig -I don't understand the comment about the use of unitstrut spring nuts. Are you referring to the hangers from the structure to the unistrut? I would think if you are referring to the pipe attachment to the unistrut via a short pipe strap with bolts and unitrut nuts that it would be acceptable since NFPA 13 2016 sec. A.9.1.1.5.2 says generic items used with hanger rods and fasteners are not required to be listed -such as bolts, nuts etc...
Reply
Bob Kluck
7/23/2021 08:26:10 am
I come from a Control Systems background, so I understand the comment. Most Electricians hang electrical boxes off Unistrut with a small piece of metal backed up/held in place by a spring. These are not really meant to hold an enormous amount of weight, and in a Sprinkler Pipe support application would likely bend and fail over time. However there are ways to have rods go straight through the Unistrut, and this would be WAY more structurally supportive.
Michael Wayne Sims
4/9/2024 12:55:23 pm
The Spring Nut is a specific component provided through Uni-Strut manufacturer. And they cannot be used for Trapeze style hangers.
CJ Bonczyk
7/22/2021 09:26:36 am
Yes unistrut is an acceptable means of support. You may want to verify from the E.O.R. that is allowed for your project though first. The manufacturers can provide modulus data in their catalogs or from their technical engineers. Also you can have a structural PE provide calculations as well although that will cost.
Reply
Dan Wilder
7/22/2021 09:50:42 am
Yes - However, I have not found many instances that Unistrut provides enough of a section modulus or weight allowance to be useful.
Reply
Casey Milhorn
7/22/2021 09:56:21 am
As others have said, yes. BUT, you will find some local or state AHJs, engineers, etc... that will fight you on it. You just have to decide if it's worth the fight, or just use pipe or angle instead....
Reply
Jessica Lutz
7/22/2021 10:18:16 am
Check your AHJ. In California, unistrut is not allowed for hanging.
Reply
Craig Hanson
7/22/2021 10:31:19 am
I have the CFC with NFPA 13 amendments but I cannot find where unistrut is not allowed. Oddly lag screws are not allowed per CFC chapter 80 NFPA 13 amendment 9.3.5.12.5 (which I have no idea why lag screws cannot be used) but I do not see anything that restricts unistrut beyond the normal exceptions in NFPA 13. Do you have a source document for the unistrut restriction.
Reply
Dave
7/22/2021 10:34:56 am
Good comments above ^^. And ditto Craig on the pipe clamps. One thing often ignored is the means of fastening said strut to the structure above, especially if the joist/truss manufacturer has particular guidelines. And don't forget NFPA #13 now requires all components of the trapeze to be sized for the pipe being supported - I still frequently see this overlooked, or special trapeze rings shown, but not installed. Lastly, while you may still pull that same old Unistrut or Powerstrut cut-sheet off the shelf or off the internets, if you list "strut" you know you may just get whatever brand your supplier or purchaser bought at the time.
Reply
Dave
7/22/2021 11:20:46 am
Dan (and I ask this with great respect for your expertise), Doesn't NFPA consider the trapeze member to be an extension of the building structure, thus the 5x does not apply? I can't find a formal or informal interpretation, but I have read this in at least one source, and the NFPA #13 trapeze tables are designed for only water-filled pipe +250. One isn't designing/certifying a hanger.
Reply
Greg
7/22/2021 12:14:31 pm
I may be wrong, but I believe the 5x plus 250 comes from the listing requirements. NFPA 13 Section 9.1.1.5 requires the hanger assemblies be listed between the building and the pipe. The requirements to be listed are 5x the weight of the pipe+250.
Reply
Dave L
7/22/2021 02:21:25 pm
For those with a NFPA #13 handbook, the commentary under 9.1.1.7 (2016) p.448, or 17.3.1 (2019) p.504, states not to include the five-times. "The requirement for trapeze hangers matches the requirement for the building structure."
Dan Wilder
7/22/2021 02:15:45 pm
Dave - Na...call me out, I'm gonna get it wrong (and I did so nice catch) and I'm fine with it (wish I could edit the statement above so others don't read and apply things incorrectly - ahem....Joe? wish list for the forum). I'm thinking my last go around with this was a shared support situation (see 9.1.1.3.1.1 13-16 Ed.), but in a sprinkler only assembly I probably lost an argument.
Reply
Dave
7/22/2021 02:33:13 pm
Ah, you just beat me to posting the commentary, Dan, probably the only time I will ever catch you on something (marking it on my calendar before Joe removes the evidence.) It reminded me I do need to re-educate myself on the difference with shared-support requirements. I was ready and willing to be proven wrong, the older I get, the more I forget and have to look things up. Honestly I never looked into why the 5x doesn't apply to trapezes. Surprised I couldn't immediately find an informal interpretation on it or an article by Victoria.
Michael
7/23/2021 08:00:38 am
What about the holes for bolts or rods requirements? How does UniStrut meet these requirements?
Reply
Dave
7/28/2021 11:49:44 am
Michael, according to a 2/17/2016 Sprinkler Age article by Tom Wellen of AFSA's Tech Services Dept. (available on-line),
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |