In a residential dwelling unit of a high rise building, would a drum light fixture (7"h x 14"d) qualify as an obstruction?
It’s a concealed head in a residential unit of a senior living building. The contractor – of course – doe not have exact dimensions because it wasn’t reflected on the plans and was added later as a lighting option and only caught by my inspectors during Rough-In. As it is installed, the head is a few inches from the fixture in some units and “a few feet” in others. They want to add a head on the other side of the light, approximately 3 feet -4 feet away citing NFPA 13 8.10.6.2.1.4. I feel that the light, while an obstruction, doesn’t count as continuous nor does it meet the requirements of a baffle, so if they want to add another head it’d have to be at least 6 feet away to prevent cold solder. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Clifford Schulze
5/7/2019 11:02:48 am
NFPA defines obstructions as both continuous and non-continuous. Can you relocate the sprinkler head to meet the obstruction criteria, in this case 2'-6" - 3'-0" off the fixture?
Reply
Rob Stewart
5/7/2019 11:08:17 am
If a residential sprinkler head - it is 8' minimum distance between sprinkler heads
Reply
pari
5/7/2019 11:19:49 am
NFPA13 D Section 8.2.5.1.1 Pendent sprinklers shall be located at least 3 ft away from obstructions such as ceiling fans and light fixtures.
Reply
Clifford Schulze
5/7/2019 12:31:59 pm
He mentioned that this is a high rise building so 13D and 13R won't apply
Reply
PETE
5/7/2019 11:23:17 am
Echo what Clifford said. The inspector is correct. The scenario you described is a non-continuous obstruction to the discharge. Per §8.6.5.1.2 in NFPA 13, the sprinkler needs to either be spaced away from the obstruction based on the table. If you look at your concealed cut sheet and find that the deflector falls 1 1/2" out of the concealed head, you'd be 5 1/2" obstructed by the light (7"-1 1/2"). That would put your sprinkler 1'-6" to 2' away from the near edge of the light. That is to spray beneath it. The other option given under that section is to sprinkler on both sides of the light. Minimum spacing rules don't apply in this option because you're treating the obstruction like a wall. In other words, because of the obstruction the sprinklers won't spray on each other. The only requirement for the 2nd option is that the sprinklers are no more than the half distance of their maximum linear spacing from the center of the obstruction, again like it's a wall.
Reply
DaviD C
5/7/2019 02:48:58 pm
Pete well stated.
Reply
Jonathan Joseph
5/7/2019 12:25:43 pm
I would agree with Pari. You must be a minimum of 8 ' from the sprinkler or fixture in this case if you choose to add a sprinkler and keep the sprinkler that is obstructed.
Reply
PETE
5/7/2019 12:45:07 pm
Anon did not state whether he was working per 13 or 13D, only that the space was a dwelling unit. Anon did state that the inspector objected to the placement per NFPA 13, so I assume it is an NFPA 13 job, not 13D.
Reply
Jonathan Joseph
5/7/2019 01:39:28 pm
It's a high-rise but the same rule applies to residential sprinklers. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |