We have a private water main feeding a combined domestic and NFPA 13 system that was specified as C900. They installed SDR21 (6") instead.
They are using the argument that this 200 psi rated pipe will not be subject to the fire system pressure and therefore is ok. I cannot find where this is listed for fire service mains. Any direction? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
2/19/2024 08:11:44 am
Most municipal water systems have underground water mains that supply both domestic and fire use and do not use NRTL fire system approved piping.
Reply
Anthony
2/19/2024 08:20:31 am
SDR -21 is covered by AWWA C605-21 I think. Thats not a recognized standard in NFPA 13 nor NFPA 24.
Reply
Scott McBride
2/19/2024 08:24:33 am
Reply
Scott McBride
2/19/2024 08:31:49 am
The approved piping is per NFPA 24 Table 10.1.1.1 and at first glance SDR-21 is not an acceptable alternative. Unless I am missing something.
Reply
Franck
2/19/2024 10:09:39 am
As indicated above, the final situation might be acceptable for its use, but it is more a liability issue and who will be responsible at the end if you accept it.
Reply
Casey Milhorn
2/19/2024 10:36:57 am
As others have said, put your concerns in writing, divorce yourself from the liability as much as possible, and move on. I assume you are the contractor and not the engineer of record.
Reply
Robert Morgan
2/19/2024 01:44:22 pm
Unfortunately our State (Illinois) health department now requires combined domestic and fire lines. We typically have a meter pit with an F-2 meter, the split occurs inside.
Reply
Mark Harris
2/19/2024 05:04:34 pm
FM approved C900 fire mains are DR14 for Class 200 and DR18 for Class 150 (think may change above 12"). I would be curious what the water company uses? If they use DR21 (which my bet is no) then like most comments above say will it work, yes. Is it correct if spec said C900 fire main, no. The lower the DR the thicker the pipe wall and higher cost per foot. If install is accepted the end user or general contractor could be justified asking for a credit. If they have to give money back maybe the site utility contractor (most likely) that installed the DR21 will read the spec next time. Hopefully they transitioned to ductile iron outside building and did not bring the plastic above through basement wall or above floor.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |