Would appreciate if you guys would weigh in on this disagreement I'm having.
Applicable Codes/Standards: The project is subject to military code UFC 3-600-01 for Sprinkler Design Area and Design Density. Otherwise, NFPA 13-2016 applies to all other aspects of the system fire sprinkler design. Description of System: The system consists of a 1,000 sqft Ordinary Hazard Design area, surrounded by a larger (remainder of building) Light Hazard design area (these adjacent hazards are separated by full height walls that are capable of preventing a fire on one side from fusing sprinklers on the other side). Per UFC, the corresponding discharge densities should be 0.20 gpm/sqft over 2,500 sqft for the Ordinary Hazard design area, and 0.10 gpm/sqft over 1,500 sqft for the Light Hazard Design Area. In accordance with the example provided in NFPA 13 Section A11.1.2, the size of the operating area for hydraulic calculations is determined by the Occupancy of the larger surrounding area. In this case, the hydraulic calculation design area is 1,500 sqft based on the larger surrounding light hazard area. A 0.20 gpm/sqft density would be provided for the 1,000 ft2 Ordinary Hazard design area, with a 0.10 gpm/sqft density for the remaining area. Differing Opinions: The difference in opinions for this situation is about how to apply NFPA 13-2016 section 23.4.4.2.5 to this situation. NFPA 13-2016 23.4.4.2.5 Where the total design discharge from these operating sprinklers is less than the minimum required discharge determined by multiplying the required design density times the required minimum design area, an additional flow shall be added at the point of connection of the branch line to the cross main furthest from the source to increase the overall demand, not including hose stream allowance, to the minimum required discharge. Opinion #1: The required minimum design area as referenced in 23.4.4.2.5 should be the SAME design area that was utilized for the hydraulic calculations as determined by NFPA 13 Section 11.2.1. In this case the minimum design area would be 1,500 sqft. Opinion #2: Even though the remote area size was determined to be 1,500 sqft per section 11.2.1, the required minimum design area as referenced in 23.4.4.2.5 should be the minimum design area for the smaller, higher hazard area. In this case, the minimum design area should be 2,500 sqft based on the Ordinary Hazard design requirements. So if the flow from the 1,500 sqft hydraulic calculation is less than 500 gpm (2,500 sqft x 0.20 gpm/sqft), then an additional flow will need to be added to the remote area to bring the flow up to 500 gpm. Which of the opinions do you feel is appropriate for this scenario? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
17 Comments
Dan Wilder
8/10/2020 09:31:28 am
Your example is very close to the A11.1.2 example and with the guidance detailed in A23.4.4.2.4.
Reply
COLIN LUSHER
8/10/2020 11:23:22 am
Thank you for your well thought out answer Dan. From an engineering perspective, it still doesn't make sense to me to add additional flow for a hazard that doesn't exist.
Reply
Dan Wilder
8/10/2020 12:49:56 pm
I would then defer to 11.6.1(3) & 12.7.2(3) showing that the intent is not to reclassify larger, lesser hazard areas for ancillary single rooms that fall within the area.
Colin
8/10/2020 01:23:27 pm
Thanks Dan!
Dan Wilder
8/11/2020 10:30:17 am
Correct as to the Hose Allowance and I would use those sections as intent that the higher hazard areas are secondary to the overall design when the room is small enough. This allows small, ancillary rooms to not drive up the remote area requirements.
Colin
8/11/2020 02:03:59 pm
Dan, you're awesome! thanks so much for the detailed explanation! I did get a ruling from NFSA that changes the way this situation is dealt with. See my comment on the main post below.
Brian Gerdwagen FPE
8/10/2020 11:33:16 am
Option #2. That is the minimum flow for Ordinary Hazard in the UFC. They could theoretically increase the hazard in the Light Hazard areas to be OH. But as this is governed by the UFC, the AHJ will have more to say about it than NFPA 13. Remember, just a few years ago, Light Hazard per the UFC was 0.10/3000, and OH was 0.20/3000.
Reply
Colin
8/10/2020 11:59:30 am
Thanks Brian. So in this example, would a small 50 sq.ft. OH2 closet within a light hazard area still trigger the same requirement for a minimum 500 gpm flow?
Reply
Franck
8/10/2020 12:01:44 pm
By using 11.1.2 and A.11.1.2, this is how I would handle the issue with NFPA (and accept it as an Insurance Company, but I am not an AHJ in your juridiction).
Reply
Franck
8/10/2020 12:13:26 pm
In addition to my above comments, I would consider § 23.4.4.3.4 & 5 only if I had a total building floor less than 1500 sq ft. Not for a mixed occupancy.
Reply
Colin Lusher
8/10/2020 01:02:50 pm
Thanks Frank! We share the same exact opinion on how to apply 23.4.4.2.4 & 5. It seems some others above do not, but I guess that is why they're called opinions.
Reply
COLIN LUSHER
8/10/2020 06:01:27 pm
I found some direction in NFPA 13 - 2019 Handbook which seems to clarify. I've only change the code references below [xx] to match the corresponding section of the 2016 version:
Reply
Colin
8/11/2020 02:11:19 pm
Thank you everyone for your input! I submitted this to NFSA an got an informal ruling in the form of an Article titled "Phantom Flow" by Kenneth E. Isman, PE.
Reply
Franck
8/13/2020 03:01:32 am
Many thanks for all the explanations.
Reply
Alan A.
2/18/2022 09:44:56 am
We are working on a large military project where the DOR is trying to push this "Phantom flow" rule on us. We've done hundreds of projects at this facility and it has never come up before. All the instances this DOR is trying to enforce this contradict what we would call common sense as well as the example given in the NFSA article you referenced.
Reply
Colin Lusher
2/18/2022 11:21:19 am
Hi Alan, yes, it must have been part of an NAVFAC or USACOE seminar last year, because this was the first I'd heard of it as well, and the DOR seemed to be unclear as to the actual application of this rule. In my case, I had to concede to the DOR/AHJ even though their application of this rule was not correct.
ALAN A.
2/19/2022 12:21:26 pm
I believe the reason no one is familiar with it, is because of how unimportant it really is. The benefit is pretty minimal as the PE explains in the article. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |