I am a President of Board of a 4-story condo building. The building was built in 1982 and is concrete block.
We received permission from fire marshal several years ago to remove all our fire hoses. The fire department told us that if there was a fire they would not use them. They would hook up to the FDC in front of our building. My question is - what is the purpose of the building's fire pump, and can we petition to also have it removed?
13 Comments
Pete H
4/4/2024 07:10:32 am
Don't get rid of the pump, they didn't tell you to get rid of the standpipe, the pump probably provides adequate flow and pressure for your standpipe system.
Reply
Anthony P
4/4/2024 08:16:38 am
Not sure which way to approach this. Getting rid of a Fire Pump (assuming this means it's a combination system) hurts your sprinkler system. Kinda also guessing by this it isn't being tested/serviced? Is the building sprinklered?
Reply
Dan Wilder
4/4/2024 08:06:41 am
Without seeing the actual language of the allowance, this is conjecture and some assumptions however:
Reply
Anthony P
4/4/2024 08:20:33 am
Good job covering all you base. There's so much to cover with something like this.
Reply
S
4/4/2024 09:32:48 am
In the Clearwater/St. Petersburg/Tampa area they are allowing fire pumps to be removed all over the place. I agree with you, very bad idea! but the Fire Marshals and Inspectors are allowing it as long as the building height requirement is met.
Reply
Glenn Berger
4/4/2024 08:19:32 am
Your question did not not inform us if there was an automatic sprinkler system installed. Also we would know if the standpipe is an Automatic or Manual Class I standpipe System. Agree that there should never be fire hoses provided for occupant or fire department use.
Reply
Jack G
4/4/2024 09:04:53 am
I would not get rid of any fire protection based on AHJ.
Reply
Jesse
4/4/2024 10:15:17 am
My first reaction is that this would a really bad idea. I'm curious to know if the building is protected by automatic sprinklers or not. The FM is right; the firefighters would never use the standpipe hose. But the fire pump is what gets the water to the automatic sprinklers and / or the standpipe outlets.
Reply
Casey Milhorn
4/4/2024 10:18:17 am
As others have said, do not get rid of the fire pump unless you have covered all the bases. I would plan on $20k minimum of engineering analysis by a Fire Protection Engineer, in consultation with a local fire sprinkler contractor. There will also be some cost to actually remove it and reconnect everything. Be warned, that the engineering analysis is likely to be money down the drain. It's a good bet that the original fire sprinkler system design was subsidized with the fire pump.
Reply
A Wiseman
4/4/2024 04:33:39 pm
Keep the fire pump! It is needed it to provide the water pressure required to serve the fire protection sprinkler system. If you remove the pump, the sprinkler system will not be able to put out a fire in the building. The fire marshal isn't going to allow the pump to be removed unless you can prove the existing sprinkler system can work without it. More than likely, it will not.
Reply
Tom Reinhardt
4/5/2024 05:18:06 am
NO.
Reply
James Art, FIre Protection Engineer
4/9/2024 01:33:58 pm
Good Old Days-Good Old Boy Fire Protection
Reply
Ricardo Gonzales Jr
4/18/2024 09:45:56 am
The answer is really simple. Have you had a Fire Protection Engineer do the analysis of the system to see IF the pump is needed? i.e. review the original design drawings and compare that to existing supply lines. If not, the word of the 'Selective Amnesia' Fire Marshal holds no water in a court situation. If a fire occurred in the complex and the sprinkler or standpipe didn't perform, the Fire Marshal would be the 1st to cite the HOA and person do made the decision then followed by lawsuits. Not worth the financial risk or jail time without a serious Engineering Analysis.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
April 2024
PE PREP SERIES |