Can a branch line tee to multiple sprinklers? Please see the attached example. I'm trying to figure out if a branch line that has a tee to multiple sprinklers would then be considered a main or still part of the branch line. This question also applies to looped branch line systems. The classification of branch lines and mains can have a major effect on the amount of seismic bracing required.
NFPA 13 defines branch lines as "The pipes supplying sprinklers, either directly or through sprigs, drops, return bends, or arm-overs." NFPA defines arm-overs as "A horizontal pipe that extends from a branch line to a single sprinkler or a sprinkler above and below a ceiling." Therefore, others that I have talked to have argued that the branch line will become a cross main since it is now feeding two sprinklers off of one line. This as a result would require additional seismic bracing. NFPA defines a cross main as "The pipes serving the branch lines, either directly or through riser nipples." In my opinion, the pipe would remain a branch line because it still aligns with the branch line definition. Moreover, there is nothing in NFPA that says that branching/teeing from a branch line automatically reclassifies the branch line as a main. Just because a pipe is no longer serving as an arm-over doesn't categorize the pipe feeding it as a main. The distinction between branch lines and cross mains is primarily based on their roles within the overall system, branch lines serve individual zones or areas, while cross mains supply multiple branch lines. What do you think? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
4/8/2024 07:22:24 am
In my opinion, yes, a branch line can tee to multiple sprinklers.
Reply
Dan Wilder
4/8/2024 08:24:26 am
In the first example, I would keep the branch line designations for both pipes. With all the definitions available, two key components that aren't directly stated is that the pipe sizing is the same and this only occurs once along the branch line. Had the pipe size been larger or more "branch lines" were being fed from the pipe, the approach becomes more blurry (I would still have called them both a branch line even with a single pipe size increase, but more than one pipe size difference would have me thinking cross main).
Reply
Franck
4/8/2024 01:16:41 pm
First, ask yourself what are the benefits of different requirements for branch lines when located in EQ areas…
Reply
Anthony
4/10/2024 07:30:59 am
Dont over think it, they're branch lines.
Reply
James Phifer
4/10/2024 11:54:53 am
It's tricky. Especially when you view the definitions of branch lines, cross amins and arm overs in chapter 3. I could see an AHJ making the case that the clouded areas are separate branch lines, and the pipes feeding them are cross mains.
Reply
Glenn Berger
4/10/2024 06:38:39 pm
The markings shown in the illustrations are correct.