During a recent site visit, I conducted a 2-hydrant flow test with the assistance of a city engineer and the fire department.
The static pressure measured at one hydrant was 84 psi, and then I proceeded 650 feet downhill to the actual flow hydrant, where the pitot pressure was recorded as 70 psi. A question arises due to the city's reluctance to test additional fire hydrants. My boss believes that testing more than one outlet is necessary to achieve a residual pressure drop. However, the city claims that their water distribution system is looped and, therefore, does not anticipate any pressure drop. As a result, we are unable to calculate consistent numbers on a graph. Additionally, we have come across information suggesting that there should be a 15 to 25% drop from static to residual pressure. Is this a compliant approach? Should we be opening up more than one outlet on the flowing hydrant? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
danefre
5/30/2023 07:42:41 am
Yes it's acceptable, but additional outlets will provide a more accurate curve. Two points on the graph are good enough for most projects. Also, you didn't indicate what the residual pressure is.
Reply
Alex
5/30/2023 08:02:37 am
To ensure accuracy, you should achieve a 25 percent pressure drop between your static and residual pressure.
Reply
5/30/2023 08:08:09 am
Well, that depends. If your flow volume exceeded the demand flow of your sprinkler system (or the NFPA 1 flow demand) then your test is adequate. Sometimes it is impossible to get a reasonable drop in static pressure due to the configuration of the system (e.g. gravity tanks).
Reply
Dan Wilder
5/30/2023 08:12:10 am
Question, was the 70 an actual pitot pressure (flowing hydrant) or was that the residual PSI from the pressure hydrant (84 static/70 Residual) with an unknown flowing GPM (not provided)?
Reply
Glenn Berger
5/30/2023 08:12:33 am
Recommendation is to follow NFPA 291 for test procedure.
Reply
Anthony
5/30/2023 02:22:47 pm
I think Glenn has it right.
Reply
Jesse
5/30/2023 08:13:27 am
Yeah you can, but opening more than one outlet gives a better picture of the water supply characteristics.
Reply
David Kendrick
5/30/2023 09:16:54 am
Looped mains are fine, knowing your supply arrangement is certainly important.
Reply
Pete D.
5/31/2023 06:47:04 am
The 25% drop rule exists for a variety of reasons. 1) Extrapolated max flows at 20 psi residual pressure are theoretical data. Interpolated points between static and residual measurements are still considered experimental data. To minimize error in the extrapolated data, is the first reason. 2) Fully developed flow- in the large diameter city network, only flowing one 2.5" butt will give something like 500-650 gpm, which may result in laminar flow in a large pipe such as 16". Once a volume flow rate is achieved that creates turbulence, there will be an exponential friction increase, which will create a drop in residual pressure readings.Turbulent flow more accurately models the water supply.
Reply
David Kendrick
5/31/2023 09:04:31 am
Pete D., Where is the 25% rule published?
Reply
Pete H
5/31/2023 09:37:11 am
Hey, I'm the wrong Pete, but I figured I'd take a stab at it.
David Kendrick
5/31/2023 09:40:08 am
Thank you very much.
Fred Walker
5/31/2023 01:28:55 pm
There is no right or wrong answer here; to large degree it "depends" on the purpose of the test. Are you getting design information to support an installed protection system which may have a 30 to 50 plus life expectancy, Assessing the health of the water distribution. Or determining available fire flow to support fire department's needs.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |