For multi family buildings, I am being told that for a 4-story building, normally the fire pumps are only 15HP because the standpipes are pressurized by the fire trucks.
My understanding of NFPA 20 is that it would still be required to have a correctly sized fire pump without considering the size of the pump on the local fire trucks. Is this an industry norm that is allowed by certain AHJ’s or is there code related to multi family that I am missing? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Joe Burtell
3/29/2024 08:13:25 am
If the standpipes are a manual standpipe per NFPA 14, city water pressure is all you need, no fire pump. The FD is responsible to provide the flow and pressure needed, pumper truck. You still need to calculate the manual standpipe. If the standpipes are required to be fully automatic, you will need a fire pump sized to provide the full pressure and flow.
Reply
Dan (WSFP) Wilder
3/29/2024 08:33:39 am
I've not done a design that changed that because of it being specifically Multi-Family UNLESS if fell outside of the scope of NFPA 13R (above 60' or more than 4 stories) as the hydraulic requirements change.
Reply
Dan Wilder
3/29/2024 08:38:01 am
and since I've read this a couple different ways
Reply
Jesse
3/29/2024 08:40:13 am
If the standpipe is a manual standpipe as defined in NFPA 14, then the fire pump (technically a booster pump unless being supplied by a static source) is only serving the automatic sprinkler system. Most of the stand-pipes my company designs are manual standpipes. Effectively we use the fire department apparatus as the water supply node.
Reply
Anthony
3/29/2024 08:40:40 am
THe building's fire pump won't be affected by the city's fire truck.
Reply
Jack G
3/29/2024 06:27:46 pm
Far from towns , buildings protected with sprinklers, would need its own tank, ( hose streams not required to be included- unless building has hoses) fire pump and standpipe hydrant with fdc.
Reply
RUSSELL BYRD
3/30/2024 12:15:03 am
Reply
Casey Milhorn
4/1/2024 09:27:15 am
As Russell stated, the FDC piping will be AFTER the fire pump discharge and it's not unnormal to have a 4" (or smaller) city water supply feeding a small 13R type pump setup but then have a 4" or 6" FDC piping system from FDC to standpipes. Think about it as the city is suppling your automatic sprinkler systems (with a booster pump when necessary) and the FDC system is supplying your standpipes/hose valves by way of pumper truck. They just happen to be partially a shared system.
Reply
Joe Burtell
4/1/2024 09:52:09 am
The problem I see here is the 2021 IBC does not allow 13R for buildings more than 30 above FDC access. If the building was not that tall we would not be talking about a standpipe system in the first place. See section 903.3.1.2 of the 2021 IBC. Maybe this jurisdiction has a different building code.
Glenn Berger
3/30/2024 07:14:03 pm
The fire pump provided for a building is not affected by the size of the pump on the truck.
Reply
Robert bennett
4/3/2024 01:08:53 pm
Additional comment to Joe Burtell, I agree with your comment with one additional observation and that is that the standpipe must still be flow tested and provide the required VOLUME prior to occupancy. Over the past 5 years we have required flow testing as indicated in NFPA 14-19 and found that 30% of standpipes, hydraulically designed failed to flow the required volume at the designers specified pressure. I would strongly recommend that you work with your local FD to test the standpipes under operational conditions to insure they will function when needed.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
April 2024
PE PREP SERIES |