Working on a new resort hotel and it is necessary to have buried pipe before and after a sprinkler control valve.
Is it allowable by code to substitute C900 PVC pipe with Tyco Blazemaster pipe? According to the installation guide of Tyco Blazemaster it could be installed underground. If not, which material can be installed instead of C900 because 4-inch is the smallest size for this pipe? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Alex
8/31/2021 07:20:26 am
Hi Anonymous,
Reply
Anonymous
8/31/2021 10:40:17 pm
Thanks for the information, Alex!
Reply
Glenn Berger
8/31/2021 08:12:39 am
***Verify the pressure losses through the underground network to the known supply point. *** 4 inch underground, while not unallowed, is atypical. Also check with the local authorities for having buried plastic pressure piping below a building slab.
Reply
Anonymous
8/31/2021 10:41:40 pm
Thanks for your comment Glenn!
Reply
John G
8/31/2021 11:12:22 am
I agree that most municipalities do not allow plastic underground. And also that the fire main be rated for 200 psi minimum. So please check local requirements and spec.
Reply
Anonymous
8/31/2021 10:44:03 pm
Thanks John! I will check if Mexico fire code allows plastic underground.
Reply
Andres
8/31/2021 10:19:06 pm
By your description, I don't think your underground pipe can fit into "fire service mains". But if that's the intent of your piping I think you can get away with it following Alex's comment. Checking both NFPA 24 and 13, neither considers CPVC for Underground Pipe.
Reply
Anonymous
8/31/2021 10:52:00 pm
Thanks Andres! As Alex said it could be an option according with their approvals. But as you mentioned, plastic pipes must be greater than 4" for fire service mains and for this new scenario ( Class 2 standpipes requirement per local code) there is no option to install a smaller supply pipe.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |