Fire alarm question for an ICC state that adopts 2012 IBC/IFC & NFPA 72, 2010 edition.
I have an existing mixed use F-1 & S-1 occupancy. This building was originally built in 1910 with two additions over the years. The building sustained fire damage a year ago and is undergoing repairs, no additions, just repairing fire damage that was quite extensive. The building is not sprinkled (not required when built). They had a partial alarm system installed about 35 years ago. The insurance will cover the cost to repair/replace the partial system only, which will require a new FACP, wiring and initiating devices. Insurance will pay for a new system to cover the entire building, if required by code. We cannot find anything in NFPA 72 that requires the entire building to have alarm coverage. There is no requirement in the IBC for F occupancies (single story, grade level) to have an alarm system. We do see where non-required systems shall be allowed to be partial. The question is, since this alarm system is being modified, is there any requirement for the entire building to be alarmed in NFPA 72? The AHJ would also like to see the entire building to be alarmed, but doesn’t think he can require it by code since it would technically be a non-required system per the IBC. The only thing he could think of was the requirement for manual pull stations at each exit since the building is not sprinkled. Any thoughts? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Chad
12/12/2023 07:00:33 am
Have you asked the AHJ yet for their input? I imagine they would help you find a way (or are you the AHJ?)
Reply
Joe
12/12/2023 08:37:09 am
You may want to review table 3206.2 of the ICC since the budling may have High pile storage, plus review the Hazmat chapters of the ICC to see if they are storing or using any materials that may require a alarm systems.
Reply
Bob
12/12/2023 09:03:13 am
In warehouses where there is packaging/light assembly, we have required partial alarm systems in the areas where the concentration of workers are present. They must have adequate exiting etc. If there are demising walls we sometimes require the entire area of that specific occupancy only. Other times just the areas subject to the increased occupant load that triggers the alarm system.
Reply
Sean
12/12/2023 09:27:08 am
IFC/ NFPA 72 does require that when you elect to add a system component, that component or feature should comply with the code. i.e. if you are installing a manual system, then pull stations are required at all exits.
Reply
Donovan Schmidt
12/12/2023 09:33:16 am
901.4.2 Nonrequired fire protection systems.
Reply
Greg
12/12/2023 12:29:58 pm
Has the owner considered the business - end user requirements under OSHA, if applicable ?
Reply
sean
12/31/2023 06:48:00 pm
consider that the consistent design is something that is discussed the code/standard.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |