NFPA 101, Section 39.2.2.2.2* Door Locking to Prevent Unwanted Entry. Where approved, doors, other than those complying with 39.2.11.2, shall be permitted to be locked to prevent unwanted entry provided that all of the following conditions are met:
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Chad
12/14/2022 08:21:28 am
Pushing the door open is not a “releasing operation”. A single knob is ok. As long as there isn’t a deadbolt, etc..
Reply
Todd E Wyatt
12/14/2022 08:26:13 am
SHORT ANSWER
Reply
Todd E Wyatt
12/14/2022 08:29:16 am
Turning the "knob" to unlatch a door is (1) motion ... pushing the door open is NOT an "additional release motion".
Reply
DavidT
12/5/2023 10:52:59 am
Yes, I agree, turning the knob is a one motion release action. This is no different than pushing down a lever or pushing a panic bar. In each example, you wil still have to push t he actual door...not included in "releasing" the actual latch.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |