I have an existing business that is approximately 4,000 sqft. It's a single-story building being renovated into an infusion center with (14) IV patient rooms.
I would consider this type of occupancy to be an Ambulatory Care occupancy because of (4) or more care recipients to be incapable of self preservation at any time. Under Ambulatory Care, this building would need to be sprinkler protected under the International Fire Code. Are these type of centers considered to fall under Ambulatory Care, or just a doctor's out patient Business occupancy? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Alex
4/27/2022 06:57:49 am
Hi,
Reply
Todd E Wyatt
4/27/2022 08:15:22 am
I concur with Alex.
Reply
Derek
4/27/2022 08:17:22 am
Agree with Alex here (as we all normally do, lol) twofold.....great question and definitely not a Group B.
Reply
Reggie
4/27/2022 08:54:37 am
What if the Infusion Center states in letter head with to the Fire Marshal Office that their services are therapies that consists of vitamins, etc. that combat auto-immune conditions that is delivered by IV due to patients unable to take oral by mouth and the patients are mobile and are never rendered incapable of self-preservation as a result of their services.
Reply
Alex
4/27/2022 02:31:17 pm
Sorry about replying with the wrong name but this response was directed to Alex and Dan Wilder. What if the Infusion Center states in letter head with to the Fire Marshal Office that their services are therapies that consists of vitamins, etc. that combat auto-immune conditions that is delivered by IV due to patients unable to take oral by mouth and the patients are mobile and are never rendered incapable of self-preservation as a result of their services.
Reply
Udo Ammon
4/28/2022 08:31:47 am
As a former AHJ, it is classified as business occupancy. Also, CMS does not recognize the less than four patients. Doesn't matter how many patients.
Reply
Dan Wilder
4/27/2022 08:22:21 am
This opens the door to much more than a requirement for a fire sprinkler system. While a good question and I'm not sure your role in the process (contractor, arch, code consultant, AHJ) there is a little grey area here as to if people are incapable of self preservation or not. Looking at a couple of my local AHJ's, there isn't a clear path between them. As Alex said, if I'm giving blood (my donation center has 14 beds in a communal space and 3 private rooms) guess whos going to leave a path for others to follow me out the building...
Reply
Anthony
4/27/2022 08:44:35 am
If its chemotherapy or another significant medication being administered then patients probably will need help exiting. I think some medications are administered under sedation?
Reply
Craig M
4/27/2022 09:03:37 am
So this one becomes tricky because you likely have more than one AHJ and if CMS Medicare and Medicare funding used at this site you likely have to follow 2012 NFPA 101 Life Safety Code.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |