I'm designing a fire suppression system for a new boiler room at an existing hospital. It will connect to the existing fire suppression piping. The hospital is served by a fire pump, but the existing pressure at the street is satisfactory to supply this particular space with enough water for Ordinary Hazard Group 2 occupancy without the pump.
Do I still need to include the fire pump in the hydraulic calculation, or can I ignore it? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Matt
4/29/2021 08:09:44 am
Can you exclude the pump - I suppose. The design will likely work. It is probably not a good idea, especially if the drawing will become part of the building record. The lack of accuracy in the drawings will likely create confusion when the plans are referenced in the future. I would put it in there.
Reply
Cameron
4/29/2021 08:15:52 am
Depending on the street static pressure and the pump churn pressure, you may just want to verify and/or document (more importantly document to cover yourself) that your not exceeding the maximum allowable pressure in you system components. I myself would include the pump in order to provide the most accurate picture of the system.
Reply
Mr Glenn Scott Berger
4/29/2021 08:16:28 am
It all depends on the piping arrangement.
Reply
Franck
4/29/2021 08:28:46 am
If your connection to your sprinkler is downstream your booster pump, I would suggest you to do both.
Reply
Dan Wilder
4/29/2021 08:47:44 am
Unless there are some pretty specific circumstances to ignore the pump (or any other fire protection feature affecting the design and layout of a system), it should be drawn to match what is installed.
Reply
Brian Hoole
4/29/2021 08:50:13 am
The pump will allow you to minimize your pipe sizes. Be sure to keep in mind that for lower floors you will either need a pressure limiting device at the floor control when boosted by the pump or to feed a riser manifold prior to the pump that will supply the lower areas.
Reply
Aaron
4/29/2021 08:54:38 am
You didn't mention whether the total water demand for the ordinary hazard II exceeds the max flow (at 150%) of the pump or not.
Reply
NK
4/29/2021 09:04:32 am
Most of the AHJ's in our area require a fire pump test report from within one year for hydraulic calculations of buildings with fire pumps. One of the big reasons is to check to see if the fire pump is performing in compliance with NFPA 25. If a pump is performing very poorly the AHJ might ask the building owner to investigate the situation even if the calculations work. Your calculations might work for this project but the the fire pump is most likely needed for a different area of the building and should be maintained per NFPA 25.
Reply
CJ Bonczyk
4/29/2021 09:19:35 am
I would suggest that you include the booster pump. The purpose of this is that in your calculation if this area now becomes the most demanding portion of the system on that floor hydraulically then you will want to ensure your new hydraulic calc plate accurately reflects the information based on what is actually boosting the system water supply. You can easily obtain a most recent copy of a fire pump test report that provides the 3 point curve indicating the suction supply along with the booster pump operating and providing the discharge pressures and flows. I would then calculate back to the discharge side of the pump using that information as your supply. It does not hurt to additionally calculate the system without the use of the booster pump to confirm the water supply works alone. Thus at a later date if the booster pump is out of service you will know what minimum water supply is needed to allow the system to work if there is any degradation in the city supply.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |