My understanding is that when using residential concealed sprinklers in a single-family (residential) home, there is an exception to beams - that we space as if they are not present. This is in the living room (image below). I think the plan reviewer is looking for sprinklers within each bay. My reading of the code was that concealed sprinklers cannot be lowered, so I disregarded the beams. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Alex
4/14/2022 07:51:35 am
Hi,
Reply
Franck Orset
4/14/2022 08:36:17 am
As outlined by Alex, you can't avoid the obstruction requirements just because they are residential concealed.
Reply
Jesse
4/14/2022 09:22:54 am
These beams may indeed constitute an obstruction. I'd be curious to know their depth. Then you'll use the obstruction rules to determine if they do or do not create an obstruction to discharge.
Reply
Jay
4/14/2022 09:27:42 am
This is regarding a single family home.
Reply
Pete H
4/15/2022 12:36:24 pm
Are the beams over the ceiling and in a concealed space? Are you in 13R or 13D?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |