We have an oil storage warehouse project requiring a ceiling density of 0.60 gpm/sqft over 3,000 sqft.
This is basically 30 sprinklers using 1,900 gpm (sprinklers), and 500 gpm (for hoses). The municipal system is set up with three pumps that run sequentially based on residual system pressure. Each pump is larger than the last. We require Pump 3 to be in operation in order to get the required flow and pressure. We have conducted a flow test flowing two hydrants, and have not been able to kick Pump 3 into action. Assuming a K16.8 sprinkler has a 3/4" orifice, 30 heads would only equal a 4" diameter opening. If we can't activate the appropriate pump by opening multiple hydrants, how will we be able to achieve the required flow during a fire? Has anyone encountered a supply system like this before? I know that a tank and pump is a solution, but I'm looking for other options. Thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
18 Comments
Dan Wilder
12/20/2021 06:34:42 am
So many questions to even start with guidance on this and you'll likely get the "Hire a professional" follow up as well.
Reply
Mike L
12/20/2021 08:14:46 am
If I'm understanding the situation properly, the municipal water supply has (3) pumps in series that activate as the pressure demand requires them to. That being the case, if your sprinkler demand is such that the municipal system does not meet your demand, then your system must include the necessary components to meet the sprinkler demand.
Reply
Jesse
12/20/2021 08:35:16 am
This actually presents a lot more in the way of questions.
Reply
OP
12/20/2021 08:36:04 am
It's a municipal system fed from a cistern. Only one pump operates at a time.
Reply
Alex
12/20/2021 11:26:38 am
Hi OP,
Reply
OP
12/20/2021 01:26:02 pm
Total flow was 3,246 @ 50 psi residual. Static at 90 psi.
David Kendrick
12/20/2021 09:58:35 am
Just an outsider's question:
Reply
OP
12/20/2021 10:18:07 am
Our initial calculations have us looking for 2,353.5 gpm @ 65 psi. With all six ports open, we were able to achieve 3,246 @ 50 psi residual, which meets our requirements. 2677.5 is available at 65 psi, provided pump 3 is operating.
Reply
David Kendrick
12/21/2021 11:16:15 am
What input are you getting from the customers underwriter?
OP
12/21/2021 11:29:26 am
The insurer has very few specific requirements - just protect it to satisfy the AHJ. We're in Ontario Canada, and our OBC points to NFPA 13, which in turn points to NFPA 30.
Franck
12/20/2021 11:00:02 am
You have to consider the avilable pressure, not only the flow.
Reply
OP
12/20/2021 01:22:21 pm
Only one pump is ever running at a time. First Pump 1, then when it's capacity is exceeded, it shuts off, and the larger Pump 2 turns on, and likewise, when its capacity is exceeded, it shuts off, and the largest Pump 3 comes on.
Reply
.Mike
12/20/2021 12:00:05 pm
Just a idea, is it possible to have the municipality manually start the 3rd pump for your test?
Reply
Casey Milhorn
12/20/2021 03:57:08 pm
Very interesting. So your water supply curve probably looks more like stairs (or 3 different supply curves in one). One ends and the other picks up. Maybe with even better pressure, or maybe less. I guess at the end of the day, as long as you have a hydrant test that proves you have the necessary pressure at system demand, there is no issue. As the system needs more, the pumps appear to operate correctly and provide more. Sounds like your follow up flow test confirms you have the adequate pressure and flow. The only concern might be is if the pressure starts out lower and ramps up, you could have a blind spot in there where a lower system demand (less heads flowing) could have a spot where pressure is too low. To me though, sounds like you have done a great job digging into the water supply and should be in good shape.
Reply
OP
12/21/2021 08:12:46 am
That's exactly it - the stepped curve.
Reply
Jay
12/20/2021 04:40:52 pm
Perform a hydrant flow test and control the flow from the ports by opening/closing the hydrants, so that you are flowing very close to the 2400 gpm that the design requires. Using the residual pressure from the hydrant during the flow test, calculate the residual pressure that will be available at the base of the sprinkler system riser. If the available pressure exceeds the design demand then the system is good to go, if not then you need to install a fire pump at the base of riser. It doesn't matter how many municipal pumps turn on, only that they turn on consistently and will provide the same pressure/flow points for the life of the building. If the municipality is constantly changing the pressures that the pumps will turn on, then that is an inconsistent/unreliable water supply that you can't design a fire protection system around, and you will need to provide the sprinkler system with its own independent and reliable water supply.
Reply
Jack G
12/20/2021 04:52:16 pm
It sounds to me that quite possibly the sizes of the municipal water mains are controlling the flow ( say like in a deluge system— can only flow so much)
Reply
sean
12/31/2021 06:27:53 pm
have you reached out to the engineering / public works dept.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |