We are on a project where they are installing these vertical storage carousels and will be storing miscellaneous vehicle parts and tires. I don't see anything within NFPA 13 specifically mentioning this equipment, so the current plan of action is to treat this equipment as multi-row racking. Since it is not practical to provide in-rack sprinklers for this equipment due to the moving parts, we are planning on protecting this equipment with ESFR sprinklers.
Does this ESFR approach seem appropriate? Is there any information that I am not considering? This is something that is new to me so any input will be greatly appreciated. https://www.storevertical.com/products/vertical-storage-system/tire-carousel https://www.storevertical.com/products/vertical-storage-system/shelving-carousel Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Franck
5/26/2021 08:18:13 am
You should check FM Global data sheet 8.34 – Protection for Automatic Storage
Reply
Craig Hanson
5/26/2021 08:18:31 am
I have just completed a very intensive review for the same type of building. I had reached out to NFSA and NFPA for clarification and deign criteria. IF you want more information please contact me at craigh@wc-3.com
Reply
CJ Bonczyk
5/26/2021 09:20:53 am
Many times when we have protected the ASRS/VLM units for tools storage we are bound by the FM Global guidelines outlined by Franck above. I would add the specific coordination with the manufacturer is heavily required. The deflector has specific distances such as 3-4 max from the carousel top. DO NOT penetrate the carousel yourself. The manufacturer will provide you will a couple options of where sprinklers can be placed. Space your sprinklers accordingly by code and ensure the penetrations are made by the manufacturer otherwise you will void the unit's warranty. Your penetration will need to be fire sealed and a steel escutcheon will need to be bolted to the top. Also a separate detection and control valve feeding the unit is required. We typically install the VSR Autotest flow switch that does not require water flow to test the system.
Reply
9/20/2022 02:52:10 pm
We are designing a fire engine maintenance facility which will include a Vidir vertical tire carousel model HT54162-0563-12. This to be located in Washington DC using the 2019 NFPA 13 code.
Reply
Kevin
5/26/2021 09:54:34 am
FM Global has Data Sheet 8-33 for Carousel Storage and Retrieval Systems as well. Not sure if the tire storage is addressed in there but is worth a look.
Reply
Dan Wilder
5/26/2021 09:59:39 am
These don't look enclosed per those links so you're likely looking at a possible ceiling only protection scheme unless a pipe can get into the center area then you may be able to have an attempt at some single/double level in-rack protection. The Case Study video of the tire carousel does show 2 levels of in-racks at about the 35 second mark.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |