I'm working on the renovation of an existing building with waffle slab construction.
As part of our scope, the client would like to sprinkler the space, and the architect was asking if we would be required to provide sprinkler coverage in each of the waffle slab pockets if they left the structure exposed. Originally I thought we could treat the space as ceiling pockets, but since it's not an "architectural feature" I'm thinking the exceptions in NFPA 13 11.2.7.2 would not apply. The pockets created are roughly 3-ft x 3-ft wide, and the structure is 2-ft deep. If we're using upright sprinklers, and they need to be installed 1"-12" below the "ceiling" (in this case, the slab?), taking a look through the obstruction/positioning tables, it seems like the structure would create obstructions and a head would be needed in every compartment? Agree? Disagree? Any insight would be appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Casey Milhorn
10/25/2022 08:09:23 am
I would recommend getting an official ruling from NFPA, and while you wait for that to come back (it can take awhile), I would get an informal interp from AFSA. I would argue this could be treated as concrete tee construction with no minimum deflector distance but with deflectors at a 1" minimum down from bottom of concrete "tee". If that doesn't fly. you can also classify this as obstructed construction, place a head at the center every 3rd to 5th pocket (depending on hazard and spacing), and keep deflector at 22" down from deck and no more than 2.5" above bottom of "tee". Sounds like you have a couple options here to avoid every pocket.
Reply
Yves Poulin
10/25/2022 08:14:09 am
Maybe if they drywall every pocket you will not need to sprinkler every waffle ?
Reply
Eric R
10/25/2022 08:44:26 am
Depending on your occupancy class I think you could get away with a 9' x 12' or 12' x 12' sprinkler spacing pattern utilizing the obstructed construction rules.
Reply
Randy Rathert
10/25/2022 10:29:31 am
Nicely done. that makes for a complete analysis.
Reply
Jessica Lutz
10/25/2022 12:00:13 pm
...Precisely how I've seen it handled on a few projects.
Reply
Alex
10/25/2022 01:40:22 pm
Exactly how I've protected waffle ceilings before in the past! Well said.
Reply
Bobby V
10/27/2022 08:53:19 am
Sections taken from 2016 NFPA 13.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |