Hi everyone - I need advice about jockey pump sizing.
The system we have has a city supply plus a booster pump. The city main shut-off pressure is 42 psi (2.9 bar) and the booster pump shut off pressure is 27.5 psi (1.9 bar). So, combined, the pressure is 69.6 psi (4.8 bar). The jockey pump pressure should be about 10 psi (0.7 bar) higher than the booster pump pressure. So, the jockey pump shutoff pressure should be 27.5 psi + 10 psi = 37.5 psi (1.9 bar + 0.7 bar = 2.6 bar)? Is this correct, or is the jockey pump shutoff pressure the combined 69.6 psi + 10 psi (4.8 bar + 0.7 bar)? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Nick D
2/10/2022 08:17:09 am
Your jockey pump stop pressure should be set at 69.5 psi. This is based on:
Reply
Glenn Berger
2/10/2022 08:17:19 am
See NFPA 20 A.14.2.6 (4)(f) for additional information. The pump starting pressure should be 10 psi different, not the stopping pressure.
Reply
Colin Lusher
2/10/2022 09:32:15 am
Nick is correct:
Reply
Alex
2/10/2022 09:37:26 am
Nick outlined the requirements well above.
Reply
Jesse
2/10/2022 09:38:13 am
Hopefully this helps from 2016 NFPA 20 A 14.2.6 (4)
Reply
Franck
2/10/2022 11:07:53 am
All the above mentioned settings are correct.
Reply
Franck
2/10/2022 11:27:38 am
Just a correction to my message (this is what happens when you answer with your phone, sorry for that…) for the last sentence
Reply
Jake
2/10/2022 11:52:33 am
Hi! I am glad that the issue sparked a debate.
Reply
Franck
2/11/2022 10:43:30 am
English is not my native language as well ;)
Jesse
2/10/2022 02:25:05 pm
Thanks for the clarification. I kinda wondered about the "shutoff" comment too.
Reply
HAHANE AROMA
5/22/2023 11:12:42 pm
Should the jockey pump be left on manual switch on/off. The property owners that I am dealing with have always been switching the pump on when they see the pressure is low and switch off when the pressure reaches the level they have marked.
Reply
lalith ramachandra
4/28/2024 07:58:17 pm
Given that water is incompressible, as soon as a hydrant is opened, the water pressure in the whole system will drop to the standing pressure?
Reply