While working in a MEP/FP firm, we are expanding to do projects in other states and learning to understand the different state requirements for Fire Protection / Fire Alarm.
What is the best way to go about obtaining each state's requirements for what is required in an upfront submittal? For example some states accept design drawings that only require denoting the hazard level whereas other require full design, calculations, and a written narrative. I understand and agree providing more detail is typically better; however, budgets can be significantly affected (negatively/positively) if only a hazard classification is required compared to a full design. Besides prior knowledge from working in a different state or jurisdiction, what is the best approach in determining what is required? Typically I start with searching what is required from the building code, but that does not always tell you what you need to submit for drawings, permit documentation, etc. It would be great to have a website that gives an example of what is an acceptable layout/design for each state. Hoping to hear any suggestions / methods that others use to determine what is required. Moderator Note: If there is significant interest in this topic, we'd be happy to open up a survey for areas that do require "full design" as an upfront submittal. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Casey Milhorn
5/10/2021 08:22:06 am
I would start with the state level websites and follow up with phone calls. But the first step would be understanding how that particular state operates for code review. If you call and ask for the design manager, or a designer, at some of the local sprinkler subs, they might be your best source of info and can usually tell you what is required for "design intent" level drawings in their area/state. Some states you will get lucky and they will review everything at the state level which makes it easier. Other states have a mixture of state fire marshal, health department, and local code reviewers that all are looking for different things, and then it can come down to even which reviewer you get. Also, some states have "dead zones" where the local doesn't know how to review or doesn't have someone designated for this. A good rule of thumb is to try and provide the majority of what is required to be on shop drawings per NFPA 13, but dumbed down a little. Most of the time this will pass muster in most areas. Gathering a comprehensive list and info would definitely be a major undertaking but I could see a benefit if there was somewhere to share this info for use by everyone.
Reply
Tony
5/10/2021 09:03:05 am
NFPA 13 (2013 Edition) Chapter 23 will tell you the differences between "Preliminary Plans" and "Working Plans".
Reply
CJ Bonczyk
5/10/2021 11:48:38 am
I would also strongly advise looking at each individual county and and city adopted code amendments and variances for both IBC & IFC where the project is located. For example here in Texas the standards used, minimum requirements, and additional requirements are vastly different from one city to another which will require a huge cost impact on what is required to be provided to the sprinkler sub at bid time. Also flow test requirements, water modeling, and so on is another issue.
Reply
Dale
5/11/2021 07:20:59 am
Experience and Trial/Error are usually how it goes. At an MEP/FP firm, they chose to not show piping for sprinklers. Had a project, and it was rejected, as we did not show the piping. Had to go back, add it, and re-submit. Some towns/cities, from experience; I know that they want to see the piping. Some towns/cities want it from the FP contractor, and are more concerned with Design Intent from the Engineer. There is really no one size fits all case.
Reply
Dan Wilder
5/11/2021 08:15:30 am
I would typically start with the minimum requested items as discussed in the below linked white paper:
Reply
Bobby Suarez
5/17/2021 10:20:52 am
In Florida, the fire protection engineering basic requirements are spelled out in the Florida Administrative Code (FAC) 61g15-32 RESPONSIBILITY RULES OF PROFESSIONAL ENGINEERS CONCERNING THE DESIGN OF FIRE PROTECTION SYSTEMS. It is an expansion on the NFPA 13 "Preliminary Plans" requirements.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |