We have a four-story project that uses NFPA 13R - 2016 Edition. There are balconies with wood structure that are getting sprinkler protection. The building is in a cold climate.
I'm trying to figure out how to correctly incorporate these balcony sprinklers in the hydraulic calculations while still being efficient in the sprinkler design (there's no fire pump on this and poor city supply). As I understand it in NFPA 13R, my options are: (1) NFPA 13R for Dwelling Unit Calculation: use dry-sidewall residential sprinklers (Reliable and Tyco have some) for the balcony. This would then be a 0.05 gpm/sqft calculation over a compartment, up to four sprinklers. (2) NFPA 13R for Outside of Dwelling Unit: use dry-sidewall quick response sprinkler for balcony. This would be a 0.10 gpm/sqft calculation for four adjacent sprinklers. The inside sprinklers could still be 0.05 gpm/sqft (per 13R), but the balcony sprinklers need to be 0.10 gpm/sqft (per 13R 7.2.2, 7.2.3). (3) If the balcony is under 500 sqft and meets a string of conditions, then dry-sidewall quick response sprinklers for the balcony can be for the compartment, up to four sprinklers (per 13R 7.2.3.1). We don't meet this here, because there are large glass slider doors over 50 sqft. Are there other options here, or is my approach for the first two options appropriate? I could very well be overthinking this. Thanks in advance. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe