Does anyone have experience in designing suppression for a warehouse that will store boats on racks?
I will appreciate any information. Which standard would even be applicable? Do we treat them like high-piled combustible storage per Chapter 32 of the IFC? What will be target hazard considering the fuel in the boat? Is there any limitation that how much they can keep inside the boat? Thanks for the input on this; I'm having a hard time on where to get started. Editor's Note: A Fire Protection Research Foundation on Marina and Boatyard Indoor Rack Storage Sprinkler Protection has been submitted and can be viewed here: PDF LINK Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
1/25/2024 07:25:06 am
Not addressed within NFPA 13 directly and should really be handled via an FPE for Design Criteria creation and/or alternates. Also, getting the insurance provider involved will be very helpful.
Reply
Pete H
1/25/2024 07:29:47 am
A standpipe system is likely required as per NFPA 303 (2016) 6.3 and 6.4.
Reply
Glenn Berger
1/25/2024 08:15:56 am
Utilizing statements made in the question:
Reply
Todd E Wyatt
1/25/2024 08:40:32 am
The Occupancy Classification (OC) determines the requirements for the automatic sprinkler system (ASPS). The storage of “boats” would be classified as a Group S-1 Moderate-Hazard Storage.
Reply
Todd E Wyatt
1/25/2024 08:46:46 am
See also "Design Criteria for Stacked Boat Storage Facility?" ... https://www.meyerfire.com/daily/design-criteria-for-stacked-boat-storage-facility
Reply
DAvid T Williams, FPE
1/25/2024 09:55:42 am
Whew... I think about all that I have learned since 2005, when we completed my one and only heated rack storage boat building (maybe four tiers high). I remember one of the main issues with the State of WI was whether a boat was a motorized vehicle that needed garage ventilation (whether fueled or not). I couldn't find my records on what I did for design, although they recently replaced the boilers. At that point we didn't have that much guidance on what to install for fire protection, so I think it was just a OH2 design. Now... what did the contractor provide? it was definitely reviewed by WI Code folks (Madison so they were tough).
Jesse
1/25/2024 12:40:58 pm
I'll reiterate the importance of involving the insurer. They'll likely assign one of their HPR loss control folks to it.
Reply
Dwight Havens
1/25/2024 02:24:50 pm
Unfortunately we have burned enough of these facilities to know they do burn. We also don't appear to have the advantage of having had fires in protected facilities, with known protection levels, which have successfully controlled. If we could find examples of facilities that were protected, but burned to the ground, or, facilities that we protected, and had a fire with successful control, we might learn something. At this point NFPA 303, an experienced FPE, and the Insurer would be your best bet.
Reply
Safety
1/25/2024 04:11:12 pm
Keep in mind when designing boat storage racks.
Reply
Dwight Havens
1/25/2024 04:41:03 pm
Excellent point. All Incident Commanders be trained to recognize this.
Reply
Joe Meyer
1/26/2024 07:25:04 am
Thankful for a contributor who emailed a copy of a 2008 Fire Protection Research Foundation Study on "Marina and Boatyard Indoor Rack Storage Sprinkler Protection".
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |