I have two large ducts 20-inches below sprinklers. One duct is 32-inches wide, the other is 42-inches wide. There is maybe 4- to 7-inches between them, only a couple inch gap on each side, running the length of a hallway.
The only rule for a continuous obstruction I can find says no coverage is needed below if the obstruction is under 4-feet. Individually these ducts aren't over 4-feet, but how does NFPA 13 address multiple obstructions like this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Mike
4/9/2021 08:08:25 am
If there is only a few inches between them and in between them, they essentially obstruct discharge to the whole hallway.
Reply
Dan Wilder
4/9/2021 08:13:32 am
While not considered a single continuous obstruction over 48", it "obstructs" up a large percentage of the available area from the ceiling/roof level sprinklers to floor coverage, additional sprinklers below would be warranted in this case (IMO).
Reply
Ray Ramos
4/9/2021 08:15:12 am
I think the obstruction rules (that has to do with size and proximity) will apply in this case, not the 4 feet rule but the other ones. Therefore you will need to add sprinkler above and below.
Reply
Jesse
4/9/2021 08:24:11 am
While you don't have a single contiguous obstruction over 48", effectively the 2 ducts act as an obstruction and will negatively affect the spray pattern from ceiling level sprinklers. I would protect underneath it.
Reply
Glenn Berger
4/9/2021 08:36:52 am
Rule of thumb - If you can't see the sprinkler from the floor, than it is obstructed and then sprinkler protection is required below the obstruction.
Reply
CJ Bonczyk
4/9/2021 09:05:42 am
A general rule of thumb in these instances (specifically corridors) I try and treat them as your would grouped obstruction similar to those addressed from FM global data sheets.
Reply
Art
4/9/2021 09:22:42 am
Maybe the intent of the code requirement for Open Grid Ceilings can be applied here. It requires 70% open and the thickness of the grid to not be greater than the clear openings. If you treat the ducts as the open grid ceiling then in your instance the gap between the ducts and between the walls does not comply and hence sprinkler coverage is obstructed and needs additional heads below the ducts. Curious what others think about this. Please let me know if you think I am way off on this.
Reply
Franck
4/9/2021 10:46:26 am
When I was still working for an insurance company and was reviewing installations (acting like an AHJ), I often asked for additional protection below grouped piping (or grouped cable trays).
Reply
ken thackery
4/9/2021 02:00:27 pm
I have seen this go both ways with small grouped ducts and cable trays. It's best to stay within the code. Also I have referenced
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |