So I've run into this a couple of places and I'm curious where other professionals land. You have a warehouse that has a mezzanine. Say the warehouse is 20'-0" tall and the height of the mezzanine is an even 10'-0".
You have 8'-0" of shelf storage underneath the mezzanine. You have 8'-0" of shelf storage on the mezzanine. You are protecting under the mezzanine separately, but the mezzanine does not make up the full floor area of the entire warehouse. So there are open areas where you only have 8'-0" of storage to a taller 20'-0" building. Does the storage over the mezzanine bring your storage up to 18'-0" or is it 8'-0" of storage? It's 18'-0" over the floor, but 8'-0" over the floor of the mezzanine. And there is protection beneath the mezzanine, but the storage under the mezzanine extends beyond the outline of the mezzanine. It's still only 8'-0" high, but now the ceiling height is different. Anyway, any input or thoughts would be great. Code references always appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Anthony
5/12/2023 07:37:20 am
Depends how wide the mezzanine is. If it's under 15' then you have to cover it as if it was the adjacent hazard anyway so the area above the mezzanine is protected at 20' height requirements.
Reply
Dewayne Martinez
5/12/2023 08:33:30 am
I would treat it the same as Anthony.
Reply
Glenn Berger
5/12/2023 08:21:06 am
Looks like you have three different issues here:
Reply
Dan Wilder
5/12/2023 08:44:41 am
They are considered separate areas.
Reply
Todd E Wyatt
5/12/2023 09:14:57 am
SUMMARY
Reply
Todd E Wyatt
5/12/2023 09:15:16 am
REFERENCES
Reply
Todd E Wyatt
5/12/2023 09:15:59 am
REFERENCES
Reply
Todd E Wyatt
5/12/2023 09:16:49 am
REFERENCES
Reply
Todd E Wyatt
5/12/2023 09:17:30 am
REFERENCES
Reply
Franck
5/12/2023 09:23:17 am
Answer is in NFPA 13
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |