We are in a fire sprinkler retrofit and we have steel joists and decking throughout the building, with mostly masonry block walls. It's a single-story structure.
Where there are doors, however, there is wood framing above the grid ceiling. How much wood constitutes an issue requiring fire sprinklers above the ceiling? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
Dan Wilder
11/30/2020 08:21:17 am
The combustible materials cannot be acting as structural elements (floors, ceilings, walls, load bearing...).
Reply
Franck
11/30/2020 10:18:37 am
Chapter 9.2.1 Concealed spaces not requiring sprinkler protection (Ed. 2019) will give you some guidance.
Reply
I'm at Work
11/30/2020 11:21:01 am
See also the relevant NFPA #13 section "Localized Protection of Exposed Combustible Construction or Exposed Combustibles"
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |