Do fire pumps typically come balanced from the factory for the desired flow and pressure?
I know they are supposed to, but (just like any other pump) is their balancing done similar to a regular pump to get the desired pressure so that the pump operates at its rated duty point? I am aware that many factors affect final pressure discharges (such as friction loss, etc.). Have you ever seen pump manufacturers calibrate pumps to the desired flow/pressure in the field? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Glenn Berger
4/20/2021 08:24:00 am
I have witnessed many factory tests for fire pumps. After installation, I have witnesses the installation testing and acceptance operations. In a super majority of the times, these tests ends up giving identical results. Less than a handful of times have there been a need to "alter" the pump characteristics to get the intended results. The cause for these alterations was mainly due to the water supply characteristics being different than previously tested. Hope this response helps in your scenario.
Reply
Dan Wilder
4/20/2021 08:55:48 am
Our pump rep has not field "field fixed" a new pump because the factory has been on point with sending out accurate curves vs field performance however, we have had underperforming pumps receive new impellers that were machined at his shop (changing the diameter) to bring back flows & pressures more inline with the original curve.
Reply
Franck
4/20/2021 09:14:48 am
Normally, for fire pumps there is no need for field adjustment.
Reply
Robert karlin
4/20/2021 10:54:36 am
Perhaps many other types of pumps are optimized for performance, as they are used for more continuous duty applications. as we all know - Fire pumps are designed to meet a particular flow - for a particular event that may never occur, and run times are limited to ITM requirements in respect to the accepted install.
Reply
Phil W
4/20/2021 11:42:20 am
As above, but sometimes poor quality flow measurement devices and pressure gauges can cause you to see different results from the factory tests.
Reply
12/29/2021 07:20:59 am
I never knew that their balancing is done similar to a regular pump to get the desired pressure so that the pump operates at its rated duty point. I never thought that it would be like this, it is really a good article. Thank you for the information about pumps.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |