We have a water storage tank and a diesel fire pump on our project.
Is there any requirement for the pressure relief valve discharge pipe, when connected to a supply tank, to be extended below the lowest possible water level? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Alex
9/2/2021 07:02:45 am
Hi Anonymous,
Reply
Jesse
9/2/2021 11:01:16 am
Agree with Alex here.
Reply
Dan Wilder
9/2/2021 08:31:50 am
No requirement but make sure to provide a means of draining the discharge pipe via a velocity check or manual valve if the piping discharge is above the outlet. Back pressure on teh discharge side of the valve can have negative affects on performance.
Reply
John G
9/2/2021 09:06:08 am
Hmmm....most fire pump problems are suction related.
Reply
10/15/2021 01:23:56 am
I would advise against the setup due to the possibility of being unable to break the water discharge.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |