Can HDPE ISO 4427, PE100 SDR 9 PE be used for underground water service pipe (dedicated for fire water), even though it carries no FM Approval?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
3/29/2023 06:44:07 am
Not on an FM designed job. But if the job is to be designed to UL or NFPA 13 standards, then it matters if HDPE PE100 meets the requirements found in AWWA C906 (Polyethylene Pressure Pipe and Fittings 4 in. Through 63 in. for Water Distribution.)
Reply
Jesse
3/29/2023 08:10:20 am
The lack of an FM approval only means it can't be used on projects governed by FM, If the project is governed by NFPA 24 you're good to go
Reply
Alex
3/29/2023 08:13:15 am
As Jesse mentioned, if the project is not FM approved, you should be good to go. You will still need to confirm with all local amendments.
Reply
Glenn Berger
3/29/2023 08:19:40 am
As others have said, if the minimum compliance is NFPA 24 you are probably good to go. Be careful when using HDPE pressure pipe. The internal diameter is not the same as cement-lined ductile pipe or even PVC pipe.
Reply
Todd E Wyatt
3/29/2023 08:59:24 am
SUMMARY
Reply
Todd E Wyatt
3/29/2023 09:38:30 am
REFERENCES continued ...
Reply
Dave
3/29/2023 08:52:48 pm
We have spec'd UL-listed HDPE pipe for a few sprinkler projects such as piers, where some physical flexibility, protection, and corrosion resistance is desired. Specs including material requirements and joining methods, but no FM requirement.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |