I am an AHJ and trying to determine if this CPVC/BlazeMaster pipe has the correct hanger arrangement. I was unable to find anything in the BlazeMaster installation manual. You can see from the photo that the sprinkler branch line hanger is attached to the building steel structural beam. However the sprinkler drop is supported by a hanger, attached to the branch line, and not to a building structural element. Is this a correct method of supporting a sprinkler drop? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
12/6/2022 06:43:04 am
I've done it with steel using the trapeze tables within NFPA 13 however I cannot find anything as to section modulus or spans for CPVC. This would be a call to the MFG or a request to the installing contractor to provide the engineering backup for this installation.
Reply
Alex
12/6/2022 07:16:37 am
Hi, as Dan mentioned above, its common with steel but I have never seen it with CPVC. I would simply ask the installing contractor to have the manufacture provide a letter stating the installation is acceptable.
Reply
Anthony
12/6/2022 08:07:40 am
Not ok without 'showing your work' if the math works out it would be acceptable. I however doubt that would be the case. That doesn't pass the eyeball test, looks like it would break with that 250lb (me) hanging from it that is required for NFPA-13 hangers.
Reply
James Phifer
12/6/2022 08:19:17 am
The appendix 2016 ed. NFPA 13: A.9.1.1.8.1 - provides the option to support sprinkler piping from other sprinkler piping where the requirements of 9.1.1.2 are met. meaning it must support the weight of the water filled pipe plus 250 lbs, Like Anthony mentioned, I doubt that would support 250 lbs.
Reply
12/6/2022 08:21:17 am
Referencing the 2022 edition of NFPA 13, Section A.17.1.3.1 states, "NFPA 13 provides the option to support sprinkler piping from other sprinkler piping where the requirements of 17.1.2 are met." I would use this verbiage to explain the intent of the Technical Committee to the installing contractor.
Reply
Glenn Berger
12/6/2022 08:33:51 am
It looks wrong and probably not originally designed this way. I would hoped to have see a pipe hanger for the branch pipe above.
Reply
Todd E Wyatt
12/6/2022 08:37:59 am
SHORT ANSWER
Reply
Jesse
12/6/2022 08:39:13 am
You can support sprinkler pipe from other sprinkler pipe presuming it supports the weight +250 lbs. Not sure that'll support it. I'd consult the manufacturer.
Reply
Randy Kimbro
12/6/2022 08:48:00 am
As usual, you guys are all awesome with the responses. I did note the 250# requirement in NFPA plus the weight of the water in the piping. And I contacted the manufacturer (BlazeMaster) as you recommended who said "absolutely not". They said their pipe must be hung from building steel/structure and never from other CPVC.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |