So the issue of "forward-flow testing" of the backflow preventers has come up a lot as of late, at least here in Massachusetts. More and more design drawings are calling for "provisions" to forward-flow test the backflow preventer. I've seen multiple ways of doing this and I'm curious as to which method is best.
One method I see is adding a bypass around the FDC check with a normally-closed butterfly valve in it. This allows you to open the butterfly valve when you want to test the backflow preventer and flush through the FDC piping. The other method I see is to extend the manifold and install a couple hose valves to use in testing. My personal opinion is that if you have the ability to run the hoses outside, use the second method. The reason for this is that if each zone has a control valve, you can shut off the sprinkler system while flushing and not introduce any of the debris in the underground into your system. By doing it the other way with the bypass, you have to mess with the FDC, and if the FDC is fed from anywhere on the system other than the end of the manifold, you can introduce debris into your system. Is this a better approach? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Alex
10/11/2021 06:26:17 am
Hi Anonymous,
Reply
Craig Hanson
10/11/2021 08:11:21 am
As a former fitter who is now an Inspector and plans reviewer. I will say the easiest way to do the forward flow test (its only done every 5 years) is to take a pup piece of piping the same size as the check valve and swap them out and test through the FDC. you will also have to take the FDC siamese off but that's no problem. This is a lot better than dragging hoses up a stairwell and connecting to the combo standpipe hose bibs and a lot less messy with no tripping hazards for residents.
Reply
Jessica Lutz
10/11/2021 10:16:58 am
This is a great solution, as long as the FDC is easily removeable.
Reply
chad
10/12/2021 07:37:12 am
The issue with that is, it requires the tester to reverse the check valve when he is done. As me how I know this gets left that way.... Laziness, mistakes etc. get in the way of this being fool proof. The bypass valve around the check with a tampered valve, at least its supervised.
Reply
Randy Kimbro
10/12/2021 03:03:34 pm
As an AHJ, the forward flow test is required ANNUALLY and usually done as part of the annual sprinkler inspection (NFPA 25 (2017) 13.7.2. MeyerFire had a great article about this in 2018:
Reply
Jack
10/11/2021 08:46:12 am
In the 80 s , when you bought a bfp, they included hose valves to test it.
Reply
CJ Bonczyk
10/11/2021 09:04:09 am
Personally if possible I like to eliminate the amount of wall penetrations as much as possible. I will make the main drain large enough to accept full flow of the backflow and tie the flushing connection into that. Then any ancillary drains (fdc ball drip, main drain, inspectors test, etc.) into a large drain manifold and make a single penetration. Thus you would have possibly only a FDC wall penetration and drain penetration. If the backflow flushing connection required is too big I just try to create a multi hose valve test connection on the manifold.
Reply
Jesse
10/11/2021 10:12:57 am
I once had the CEO of a Fortune 500 tell me, "it doesn't matter who pays the green fees, just that the green fees get paid".
Reply
Dave
10/11/2021 10:48:23 am
For comparison, whether the backflow is inside the building or out in the yard, we spec incorporating full forward-flow test valves as part of the riser manifold assembly, starting with a normally closed butterfly w/tamper switch* , THEN to the required quantity of 2-1/2" hose valves, penetrating the wall. Like CJ, I'm not a big fan of additional wall penetrations, but this is our preference. If this does not result in the hose valves penetrating safely into a service yard, if theft might be an issue, or in certain education or healthcare situations, I will keep the hose valves inside the riser room with the hose discharges directed towards the riser room door to the exterior and hopefully they bring intact hoses. Where theft might be an issue, I've seen 2-1/2" grooved caps installed through the wall with loose grooved hose valves supplied in the riser room. I've also seen low-bid sub just install a capped shaped nipple on the manifold and say there is your "means" - Not good.
Reply
Mike
10/11/2021 10:57:49 am
I've designed downstream test manifolds similar to fire pump test headers.
Reply
Bruce Seiler
10/11/2021 01:03:22 pm
We have done many of the comments above. I personally do no like utilizing the FDC. As mentioned above, in order to gain the full flow from the outlet, you need to removed the FDC unless it is a Storz Connection. I like the idea of connecting the test discharge to the a drain existing the building. We do this as part of our standpipe system testing where we upsize the drain and utilize that to discharge the water outside.
Reply
Anonymous
10/12/2021 05:01:55 pm
"Question. What type of equipment is everyone using to perform this test?"
Reply
David
10/13/2021 05:22:51 pm
Most of the time I see the main drain sized to accommodate the system demand, or an FDC bypass is used (only one outlets flows because of clapper though). I use a pitot gauge to measure the flow.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |