For a flight simulator inside a larger building, what sprinkler density do you feel would be appropriate for this hazard?
The simulator will be its own contained unit, so the top will likely shield water spray from sprinklers above and prevent water penetration to the inside, much like a vehicle fire would in a parking garage. NFPA 13 does not address simulators, nor does UFC 3-600-01 or FM Data Sheets (as far as I can tell). In my opinion the closest hazard I can gather would be vehicles in a parking garage which carry an Ordinary Hazard Group 1 designation under NFPA 13 (2016) 5.3.1 and A.5.3.1. Posted anonymously for discussion. Discuss this | Submit a Question | Subscribe
10 Comments
Dan Wilder
4/23/2019 10:15:03 am
Can't you use the criteria out of UFC 4-171-01N to apply to this single room (or rooms)?
Reply
WES
4/23/2019 10:39:31 am
I would think UFC 4-171-01N, but there's no specific criteria for sprinkler systems protecting simulator facilities:
Reply
Franck
4/23/2019 10:16:59 am
As far as I can remember, this is addresses in one of the Factory Mutual Data Sheet
Reply
Franck
4/23/2019 02:25:26 pm
I found it: FM data sheet 7.3
Reply
Franck
4/23/2019 02:32:44 pm
Once you have protected the hydraulic units (normally in a separate fire cut-off room) with sprinkler for EH occupancy and the computer systems and flight simulator cabin with gaz, do you really need to protect the room ?
PETE
4/23/2019 10:19:44 am
Ordinary Hazard may cover the simulator, but it sounds like it is expensive enough that they won't want it to get wet. CeaseFire makes a Class ABC automatic extinguishing system (dry chemical). Also, a Fike FM200 clean agent may be an appropriate system. You may be able to get away with placing a fire extinguisher in the flight simulator. That would be covered under equivalency 1.5.2 and must be approved by the AHJ. That might be my first approach.
Reply
Tom
4/23/2019 10:39:30 am
I did some commissioning for some flight simulators. The computer rooms were all protected with a fike FM200 system. The flight simulators were either hydraulic oil or electric motor. The flight simulators themselves had deluge sprinklers located on the ground pointing up at them. There was a VESDA system at the roof level of the simulator bay. I can't recall if there was a suppression system at the roof level of the simulator bays...had to be a sprinkler system though. They also used flame camera detectors to watch the hydraulic simulators.
Reply
Franck
4/23/2019 02:36:15 pm
The deluge from the ground pointing at the simulator is to protect the hydraulic oil located below the cabin... the hydraulic unit might be located in a separate cut-off room, but hydraulic piping is also present at the simulator area...
Reply
Mike
4/23/2019 11:23:42 am
I think Pete has the right idea. Those sims aren't cheap and probably would be better protected with a clean agent system.
Reply
Daniel Garcia
4/23/2019 11:43:19 am
I used to work for the corps of engineers and I remember that it was an HSSD (high sensitivity smoke detection) system that was put in these. I don't remember suppression inside but it doesn't mean there may not be a need for it. I'd also check Air Force Engineering Technical Letter (ETL 01-18). It might have some additional information that you find helpful.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |