Is a Pathway Survivability of Level 1 allowed for an elementary school and high school?
If not, what kind of protection would be required? Are there any performance alternatives? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Fellippe Galletta
6/21/2023 08:19:51 am
To answer this question properly, we would need to know the applicable building code — 2021 IBC? K-12 typically require voice systems in the newer codes (occupant load over 100 with some exceptions), but unless the voice system is required to employ partial evacuation or relocation, one wouldn’t need a Level 2 or 3 survivability (I.e. 2 hour rated pathways with/without sprinkler protection). If it’s a high rise school then it would need a level 2, most likely 3 survivability.
Reply
Todd E Wyatt
6/21/2023 08:47:45 am
"Pathway Survivability" is addressed by the referenced standard (e.g. 2022 NFPA 72 National Fire Alarm and Signaling Code) per the adopted scoping Code (e.g. IBC).
Reply
Todd E Wyatt
6/21/2023 08:48:43 am
REFERENCES
Reply
Todd E Wyatt
6/21/2023 08:49:40 am
REFERENCES continued ...
Todd E Wyatt
6/21/2023 08:51:23 am
REFERENCES continued ...
Todd E Wyatt
6/21/2023 08:52:57 am
REFERENCES
sean
6/21/2023 01:34:30 pm
Pathway survivability kicks in with protect in place, relocation, or partial evacuation.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |