I was searching for an answer to question that was asked about limited area fire sprinkler systems.
Is a Fire Department Connection required for a limited area fire sprinkler system? The application that we have is a single sprinkler head installed in a medical gas closet. From my code research (IFC 2015 903.3.8 with amendments), it appears that a limited area system can be run off of the domestic water supply and thus omits a need for the FDC and other devices associated with a full sprinkler installation. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
John Lane
8/11/2020 11:29:45 am
NFPA 13 Section 8.17.2.2 (2013 Ed.) States the following systems shall not require a fire department connection:
Reply
Jonathan Sullivan
8/11/2020 11:44:29 am
Also check with your AHJ. Likely they will allow #3, but it is worth getting their buy in.
Reply
Mark C.
8/12/2020 10:41:42 am
I believe you did answer your own question. IFC 2015, Section 903.3.8.3 says you can pipe the sprinkler from the plumbing system, which eliminates the need for an FDC. If the building has a wet standpipe system installed, the limited area sprinkler must be supplied from that, which would require an FDC for the standpipe system.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |