Architect here with a fire code question. We have a fully sprinklered building (ESFR), of Type II-B, tilt concrete construction.
The fire pump room is located on an exterior wall, and the only door into the pump room is from the exterior. We have 1-hr rated construction separating the fire pump room from the rest of the building. The fire marshal is telling us that the exterior wall and door also have to be rated. I responded by pointing out the fire pump is required to be protected from the surrounding building, and that it does not need to be protected from the exterior, so exterior wall and door should not have to be rated. Fire marshal disagrees and pointed to NFPA 20 4.14.1.1.2. That section does not specifically state that separation is required from the rest of the building, although Section 4.14.1.1.1 right before it does make that distinction, just like IBC/IFC do. We have solid concrete walls that are inherently fire rated construction, so typically I would just say ok and label them rated. The issue is we are required to have ventilation in the pump room per NFPA 20, so we have a makeup air louver in the exterior wall. If we rate the wall, then my understanding is we will have to put a fire/smoke damper on that louver, which is added cost and unnecessary in my opinion. Is your understanding that all walls have to be rated as the fire marshal is saying, or just the walls between pump room and rest of building? I've done many buildings of this type in multiple states and this is the first time I've been told this. I'd appreciate your insight, thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
7/20/2023 07:28:09 am
TL;DR: Its reasonable for a fire official to intemperate table 4.14.1.1.2 as the full pump house connected to the building.
Reply
Todd E Wyatt
7/20/2023 08:26:07 am
The Exterior Wall (EW) of the Fire Pump Room (FPR) is not required to have a fire-resistance rating (FRR) per the scoping Code (e.g. 2021 IBC).
Reply
Dan Wilder
7/20/2023 08:34:57 am
Not an IBC guy but....
Reply
Scott Keeley
7/20/2023 08:45:01 am
As an AHJ, he is misinterpreting this section of the code. The exterior wall is not required to be rated. You could always file an appeal and take before the AHJ's construction and appeals board.
Reply
Glenn Berger
7/20/2023 08:53:55 am
From what you have said, you should be good from your building. You have not made any discussions on the surrounding buildings or other external equipment, for which protection may be required.
Reply
Jesse
7/20/2023 09:55:17 am
I'm gonna jump in with Glenn here. Is there an exterior exposure involved? Yard storage, Wildland-urban interface, exposing buildings with no adequate clear space separation?
Reply
CJ
7/20/2023 09:07:51 am
I think that Todd briefly touched on the most helpful fact above… even if the exterior wall was rated, the louver would not require a fire damper (unless it’s right next to a means of egress). If the mechanical engineer says otherwise, let me know and I can dig out the codes sections.
Reply
Franck
7/20/2023 09:42:44 am
Unless you have idle pallets (or other combustible load or building) close to the exterior wall, I don’t see any reason for fire rating requirements.
Reply
Sean
7/20/2023 11:00:54 am
I think the NFPA 20 is pretty clear. 4.14.1.1.2 says "protected by fire rated construction", but Table 4.14.1.1.2 is specific in saying that the fire separation is required between the protected building and the pump room. The exterior is not part of the building, so no separation is required. Handbook commentary in the 2022 edition also clarifies this.
Reply
I will add in from a building code perspective since most others discussed the NFPA standards. In general, exterior wall ratings and allowances for openings originate from Table 601 and Section 705 from the IBC. These requirements stem from construction type and fire separation distance. The vent for the exterior wall could fall under the requirements of Section 705 for unprotected openings. If the other advice is not working, this may be an alternative solution by stating what your allowance is for unprotected openings for that wall based on fire separation distance.
Reply
Janak Patel
7/26/2023 12:01:09 pm
Per NFPA 20 (2019), Table 4.14.1.1.2, a fully sprinklered Pump Room separate from a fully sprinklered building (non-high rise), the exterior walls need to be at least 1 hour fire rated or 50 ft separated.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |